Home built in 1990, no modifications, etc.
Breakers are all type HOM Square D. Load center is an I-T-E Siemens brand.
Are these breakers allowed in a Siemens box?
(Searched the BB but am in need of a quick response, sorry but thanks!)
Home built in 1990, no modifications, etc.
Breakers are all type HOM Square D. Load center is an I-T-E Siemens brand.
Are these breakers allowed in a Siemens box?
(Searched the BB but am in need of a quick response, sorry but thanks!)
Did you read the label in the box? When a manufacturer restricts use to his breakers, that is where he publishes it?
Yes. Note reads: … designed for use with only I-T-E type QP, QT, QPF, QPH, QPHF, and HQP circuit breakers. All others will void warranty.
So, probably a dumb question, aside from the warranty issue, are HOM Square D breakers allowed?
(Yeah, this seems like a dumb question as I write it but maybe allowable alternates can now be used…)
:ack:
Thanks, now after reading that, would you write up the panel as I described? Sorry, long day and a bit cross eyed right now :ack:
Robert this was posted before, Square D 1-pole HOM 115 thru 150 and 2-pole HOM 215 thru 250 are compatible with ITE Siemens.
Gary
I’ve been out for a bit.
I simply state that the panel has breakers installed that are not on the list marked on the label and include a photo of the label.
Refer it out to a qualified electrician and let him sort it out.
If you want to do some more digging call ITE and ask them.
At this time Square D breakers are only listed for use in their panels.
Thanks Mike and Gary (Gary, Thx for the email too)