Question. What's the point of this? Why not connect the feeders directly to the terminals under screw lugs (as the neutral already is)?


--
Jeff Pope
JPI Home Inspection Service
"At JPI, we'll help you look better"
(661) 212-0738

Originally Posted By: jtedesco
This post was automatically imported from our archived forum.



Jeff: I believe that is a “Back-Fed Device”


Plug-in-type overcurrent protection devices or plug-in type main lug assemblies that are backfed and used to terminate field-installed ungrounded supply conductors shall be secured in place by an additional fastener that requires other than a pull to release the device from the mounting means on the panel.

![icon_smile.gif](upload://b6iczyK1ETUUqRUc4PAkX83GF2O.gif)


--
Joe Tedesco, NEC Consultant

www.nachi.org/tedescobook.htm

Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



Yup


I believe this is just a way to use a main breaker panel as a main lug panel and save the price of a big breaker. Probably saved him $40.


They also make something that is only rated as a disconnect with no overcurrent protection. It has a “blank” handle where the “amps” usually go. You see them in disconnect panels for AC units a lot.