680.74 Bonding All metal piping systems and all grounded metal parts in contact with the circulating water shall be bonded together using a copper bonding jumper, insulated, covered, or bare, not smaller than 8 AWG solid.
The motor should be grounded/bonded by the EGC with the branch-circuit feeding the tub.
I agree that it’s poorly written and that Mike’s guys are wrong on this one. Hopefully the 2014 NEC will clear this up a bit. Here’s a proposal that has so far been accepted.
I would guess that maybe sometimes the heater is added later so a bonding jumper can be installed between the motor housing and the heater. If the manufacturers instructions are part of the listing then they must be followed even if they exceed the requirements of the NEC.
I have seen instructions like those that created a code violation if they were followed. It seems that often times they were written by someone with limited knowledge of the NEC. As that is written it calls for grounding when the correct term would be bonding. The grounding is taken care of by the circuit EGC, not a #8.
The tub also does not require a bonding grid under it like a hot tub AFAIK. The lug would be used if a bond grid were in place.
Thanks for posting that section Mike. I see while reading it that this was a change to the 2011.
How is the water getting into the tub? If you say by the pipes that supply the water to the tub then this must be in contact with the water that is being circulated would you not say.
Let’s look at what is being said;
All metal piping systems
and
all grounded metal parts in contact with the circulating water shall be bonded together using a solid copper bonding jumper, insulated, covered, or bare, not smaller than 8 AWG.
The water cannot get into the tub unless it comes out of the piping system and it is possible and probable that the water can fill while the tub is on therefore requiring the tub to be bonded to the supply piping.
The mixing valve is exposed to anyone in the tub at all times therefore the supply pipes needs to be bonded.
What we need to keep in mind is that this bond is installed to protect the person in the tub and to keep everything at the same potential. It is not a fault clearing bond.