So I have a Siemens 100 amp panel which is equipped with 2 additional bus bars for grounding / neutrals. There is no visible jumpers to the additional bus bars.
Should there be jumpers here or is the connection to ground/neutral through the panel cabinet sufficient?
The bond is accomplished with the green bonding screw on the right buss.
Assuming this is the service panel, you can land the grounds and the neutrals on the neutral bars bonded to the panel via the green screw. You cannot, however, land neutrals on those extra grounding bus bars as that would make non-fault currents go through the panel enclosure. In your example, I don’t see any neutrals on the ground bars, so no issue in that regard.
Thanks Guys!!
The EGC bus is connected to the cabinet by the mounting screws that’s all that’s required.
Thanks Robert!
Is this a sub or a main?
Wire crossing over power buses.
Robert, Do you see an issue with that? I dislike that method but it’s factory installed jumper.
Yes. Even though the the bonding means is solid and insulated, it is a risk nonetheless. It would be much safer to reroute bonding around the buses.
It’s a UL listed panel, nobody’s rerouting it. You’re being silly. The issue is with field installed wires flapping in the wind over and across the bus, not a factory secured and tested tie bars. May not be the best design, but it works fine in thousands of panels.
Main (Service Equipment)
Service panel. The 3 wire feeder is the clue.
You are being silly. The conductor plainly crosses the buses. The manufacturer left an idea monkier for home-owners and handymen. It would be just as easy for the manufacturer to bond the neutral busses in a fashion that would be safer.
An insulated conductor in front of the bus is not a hazard. It is not going anywhere… The panel is listed that way.
The exposed lugs are more of a hazard.
Hi Simon and others,
I will like to circle back to this statement about landing the neutral wires onto the additional bus bars that are attached to the main cabinet panel. I have called that out and the electrician is arguing that the bonding screw which is touching the panel is essentially connecting the additional bus bar that is attached to the panel. I am having a hard time finding (most likely not using the correct terminology) to back up this argument. Can someone please help confirm that this picture is or is not acceptable. Many thanks.
You are correct. The bonding screw and the enclosure is not to be used to extend grounded conductors by connecting them to the grounding bar. Is this a master electrician or someone who works for one? too many “friend”, uncle BOB, electricians out there.
NEC 200.2(B)
Thank you for clarrifying
Exactly, unfortunately in my state, anyone really can do any electrical work in a residential remodel without any permits/ code enforcement in a lot of these towns.
Thanks again
By placing a neutral on a ground bar you are putting current on the enclosure and other metal parts and creating a shock hazard.
On a remote distribution panel, no?