Originally Posted By: dbozek This post was automatically imported from our archived forum.
I agree with Todd that it is overkill and actually overprotection. The device should be protected with a 15 amp breaker. The 10 gauge wire is good for 30 amps but again no need for it to be wired with it. 14 gauge would be sufficient for such is rated for 15 amps in a residential environment. However, the wire size is not nearly as important as the device protecting it. Chances are, whoever installed it, didn’t have anything other than 10 gauge wire. The best install here would be 12 gauge wire on a 15 amp breaker. 8 amps is about the most that heater would draw.