"P2803.6.1 Requirements for discharge pipe. The discharge
piping serving a pressure-relief valve, temperature relief
valve or combination valve shall:
Not be directly connected to the drainage system.
Discharge through an air gap located in the same
room as the water heater.
Not be smaller than the diameter of the outlet of the
valve served and shall discharge full size to the air
gap.
Serve a single relief device and shall not connect to
piping serving any other relief device or equipment.
**5. Discharge to the floor, to the pan serving the
water heater or storage tank, to a waste receptor
or to the outdoors. **
Discharge in a manner that does not cause personal
injury or structural damage.
Discharge to a termination point that is readily
observable by the building occupants.
Not be trapped.
Be installed to flow by gravity.
Not terminate more than 6 inches (152 mm) above
the floor or waste receptor.
Not have a threaded connection at the end of the piping.
Not have valves or tee fittings.
Be constructed of those materials listed in Section
P2904.5 or materials tested, rated and approved for
such use in accordance with ASME A112.4.1. 438"
I think that was the point of the thread… It’s been discussed here several times, and the conclusion was that it couldn’t. Apparently now there is a change that allows it.
I think it’s a question of volume. If a TPR discharges it’s going to be under pressure. While the drain in the pan is likely the same size as the TPR discharge, it is only gravity fed. Therefore the pan will fill up and overflow.
In my opinion it really isn’t going to matter much one way or the other. If the TPR is dripping, the pan will be sufficient. If it’s discharging, it’s going to be splashing all over everything anyway, so the pan is going to likely be redundant.
Ben Gromicko even has a training package somewhere that say’s it’s prohibited because the pan doesn’t meet the definition of a waste receptor because the size of the drain pipe wouldn’t be able to accommodate a full discharge from the water heater. At least, that was the logic. I suppose the plumber and home builder’s lobby got it changed.