wdecker
(William Decker, CMI, IL. Lic. 450.002240)
June 13, 2006, 11:02pm
1
Ran into a house with a cat 1 furnace in the attic. The exhaust was properly vented.
The problem was that the attic was filled with blown in cellulose insulation and it was very friable. There was a vent for combustion air to enter, but it was full of this insulation.
I told them to run an intake air duct.
Ridge vents and soffit vents.
Opinions.
bking
(Bruce A. King)
June 14, 2006, 2:28am
2
Good catch, no matter what, if there is a problem occuring it should be reported and details provided to prevent a sub from sidestepping the issue.
jhagarty
(Joseph Hagarty, CMI)
June 14, 2006, 5:28am
3
wdecker:
Ran into a house with a cat 1 furnace in the attic. The exhaust was properly vented.
The problem was that the attic was filled with blown in cellulose insulation and it was very friable.** There was a vent for combustion air to enter, but it was full of this insulation.**
I told them to run an intake air duct.
Ridge vents and soffit vents.
Opinions.
The cause for concern is demonstrated.
The need for further review and/or repair is justifiable.