Chimney Height
Originally Posted By: dmacy
http://www.nachi.org/bbsystem/usrimages/5/52505_Strongsville_005_Small.jpg ]
Thanks
Dave
Originally Posted By: jpope
That would be a gas appliance, correct? Not a true, wood burning fireplace.
Jeff Pope
JPI Home Inspection Service
“At JPI, we’ll help you look better”
(661) 212-0738
Jeff
Yes it is for gas appliances.
Thanks for taking the time to answer my posts.
I value your expertise.
Dave
Originally Posted By: aleleika
David,
The chimney needs to be 2' above anything within 10'
I don't have an illustration for you, maybe someone has a code check book illustration that they can post?
A. Dan Leleika
www.a-teamhomeinspections.com
Because this is a gas appliance, not a “real” chimney, it follows the 8 foot rule (10 and 2 for a chimney).
Depending on the slope of the roof, it is required to extend from 1' to 8' vertical.
A roof pitched at 8/12 to 9/12 would require an extension of 2'. Anything less than 6/12 requires only 1'.
Jeff Pope
(661) 212-0738
Jeff,
Where can I find this 8' rule....I have only reference material that states even with gas appliance flue pipes must follow the 10' rule.
Any help would be appreciated, Thanks.
A. Dan Leleika
Quote:
IRC G2427.6.5 (503.6.6) Gas Vent Termination. A gas vent shall terminate in accordance with one of the following.
1. Above the roof surface with a listed cap or listed roof assembly. Gas vents 12 inches (305 mm) in size or smaller with listed caps shall be permitted to be terminated in accordance with Figure G2427.6.5 provided that such vents are at least 8 feet (2438 mm) from a vertical wall or similar obstruction.
continued. . .
All other gas vents shall terminate not less than 2 feet (610 mm) above the highest point where they pass through the roof and at least 2 feet (610 mm) higher than any portion of a building within 10 feet (3048 mm).
Jeff Pope
(661) 212-0738
A. Dan Leleika