Can a high efficiency gas furnace located in an unfinished attic draw it’s combustion air from the attic or is the intake air required to be from the exterior?


The exhaust vent on said furnace went through the roof. Why did they not bother with extending the intake as well?



www.overbrookhomeinspection.com


It’s not over till you’re underground

Originally Posted By: rcloyd
This post was automatically imported from our archived forum.



Matthew:


It is permissible to draw the combustion air from the attic as long as:

1) The attic provides the necessary volume of combustion air.

2) the combustion air opening shall be provided with a metal sleeve
extending from the appliance to at least 6 inches above the top of
the ceiling joists and insulation.
3) The end of the combustion air inlet duct shall not be screened.

Regards,


--
Russell G. Cloyd
Intra-Spec Home Inspections
& Code Consulting, LLC
859-586-4591
www.intra-spechomeinspections.com

Originally Posted By: mbartels
This post was automatically imported from our archived forum.



Thanks for the reply icon_wink.gif


The attic was huge and well ventilated so I don’t think the amount of air would be a problem.