That’s a pretty freaking weird panel. That’s not a 4-pole main breaker. That’s two, two pole breakers. One, for a subfeed breaker, and one to take care of the branch breakers in the lower section. A 200 amp feed hits those main lugs on top, then it goes through two double pole, 100 amp breakers. That’s 100 amps for the subfeed breaker, and 100 amps for the branch breaker buss below.
It appears the main breaker on the left there is double-tapped. Once, for another subfeed, and once to go down the the buss for the branch breakers.
Dang, Marc, you must LIVE on this board!! LOL!! Anyway, for the record I concur with your assessment. Gotta call out that double tap…as if there was no way to avoid it! Geeze!
Marc,
The reason I called it a 4 pole was because I could not trip each double pole independently. All 4 trip together,… and I could not find out where they tied together other then possibly internally and hence my deduction of a 4 pole.
Thanks for your insight!
“Howard, Fine, and Howard Electrical at your service” … nyuk, nyuk, nyuk…
Can’t make out whether the bottom left terminals are double-tapped or they are hard-wired connection off the mains passing under the “quadruple pole” breaker to the bottom bus… were they double-tapped, Peter?
This is similar to many Siemens 200 amp main breakers. They used to use two 100 amp breakers in parallel to get the 200 amp two pole. All four handles were tied together.
I have one in my own home.