I was at an inspection yesterday and I noticed that there was a lot of condensation at the air handler in the home. So much so that it was dripping from the suction and refrigerant lines onto the closet floor where it was located. I noted to have a A/C professional further evaluate the problem, but I would like to know what could possibly be causing this problem. The A/C tested well as far as temperature. What do you think?


Originally Posted By: aleleika
This post was automatically imported from our archived forum.



Possibly a leaking condensate tray over the heat exchanger. It could have rusted or the condensate tube is clogged.



A. Dan Leleika


www.a-teamhomeinspections.com

Originally Posted By: dandersen
This post was automatically imported from our archived forum.



Got a Pic?


If the insulation on the suction line does not extend to the coil, it will condense water and drop into the furnace.

Also, where the lineset enters the cased coil is a common site for supply air leakage. This will condense water on anything it blows on.

Also, Also if foil tape is used to seal this opening, the tape will conduct heat and sweat also.

There can be other things, but need to see a PIC first.


Originally Posted By: tallen
This post was automatically imported from our archived forum.



pmagrone wrote:
I was at an inspection yesterday and I noticed that there was a lot of condensation at the air handler in the home. So much so that it was dripping from the suction and refrigerant lines onto the closet floor where it was located. I noted to have a A/C professional further evaluate the problem, but I would like to know what could possibly be causing this problem. The A/C tested well as far as temperature. What do you think?


It seems that sometimes the humidity is soooo high that condensation is inevitable.

Make sure the drain pan is ok and the condensate lines are flowing, if they are not call for an HVAC tech.


--
I have put the past behind me,
where , however, it now sits, making rude remarks.

www.whiteglovehomeinspections.net

30 Oct 2003-- 29 Nov2005

Originally Posted By: dandersen
This post was automatically imported from our archived forum.



Quote:
So much so that it was dripping from the suction and refrigerant lines onto the closet floor where it was located.


The humidity should not be high in the indoor closet if the unit is working correctly.


Originally Posted By: bkelly2
This post was automatically imported from our archived forum.



Leak Under Air Handler ]



“I used to be disgusted, Now I try to Be amused”-Elvis Costello

Originally Posted By: pbolliger
This post was automatically imported from our archived forum.



Other possibilities are:


Plugged condensate drain line, Poorly connected drain line to tray or loose altogether. Bad slope on the line or even non- glued joints together..