Is this a problem?

Originally Posted By: Heath Brier Johns
This post was automatically imported from our archived forum.



The cooling unit in the crawl space was condensating on the bottom of the unit big time. The pad it sits on was drenched, any takers?


[ Image: http://www.nachi.org/bbsystem/usrimages/W/Woodard_photos_011.jpg ]
[ Image: http://www.nachi.org/bbsystem/usrimages/W/Woodard_photos_010.jpg ]


Originally Posted By: jjackson
This post was automatically imported from our archived forum.



Condensate line plugged or broken?



jj

Originally Posted By: Heath Brier Johns
This post was automatically imported from our archived forum.



The line was not broken or plugged. The line did have fungus growing around it.


Originally Posted By: bgentry
This post was automatically imported from our archived forum.



Without being there, of course, I would also say there is a problem with the consensate line or pan. If you can’t find a reason for it, then I would defer to a heating/cooling specialist, which I’m sure you did.



Bradley S. Gentry


Superior Home Inspection, LLC


Harrisonburg, Charlottesville, &


Elkton, VA


www.superiorllc.net

Originally Posted By: jsmith10
This post was automatically imported from our archived forum.



I’d say that one likely scenario would be that the discharge line was higher than the pan since it is in the crawlspace.



Joe,


Vice-President, Idaho Chapter,


www.NachiIdaho.org


Inspected as though my family are to live or work there.

http://www.Treasurevalleyinspections.com

Originally Posted By: kbowles
This post was automatically imported from our archived forum.



There must be significant air leakage around the coil cabinet and the furnace itself. This is appears to be condensation guys not a leaky condensation line. Coil cabinets will do this when there is enough air leakage around the take offs from the plenum. On a warm humid day, the cold air will blow on the cabinet and viola, condensation, puddles, mold, and all kinds of other good stuff.Obviously a moisture problem to have a dew point that forms that kind of condensation on a cabinet. Insulating the cabinet with ductwrap will certainly help but this would need to be done during the heating season as not to trap in moisture that is already present. And if that is the bottom of the furnace, which you couldn’t wrap with duct wrap, then there is definitely an air leakage problem since cold air should never be on that side of the coil. I would also check the humidity levels of that crawl, I would guess around 70% or better with that going on.



Life’s a journey, not a destination.


Aerosmith

Originally Posted By: jwilliams4
This post was automatically imported from our archived forum.



Give that man one silver cigar(kbowles) I’ve seen this a number of


times. I gets very humid in those crawls in Cinci. I’ve found some


equipment that was short on insulation(factory defect)



“not just an inspection, but an education”

Originally Posted By: Blaine Wiley
This post was automatically imported from our archived forum.



That looks simply like condensation from the cold cabinet being installed in a damp warm environment. I find that consistently here in humid area installations (garages, crawl spaces and attics). Definitely causes the cabinets to rust out prior to the average useful life!