jbushart
(James H. Bushart)
June 4, 2010, 4:21pm
HVAC specialist question:
During fire up and prior to blower, flue gases measured 9.0 Oxygen, and 75.6 XAir. After blower, O2 went up to 9.6 and XAir to 85.0.
Is this enough of a change to indicate a cracked air exchange? Is there an acceptable range published somewhere?
jbushart:
Definitely communication from the pressurized house air side of the heat exchanger to the combustion gas side. May be cracked exchanger or bad gasket, if any installed. IMO, should be called.
Bacharach in their literature calls out any change in oxygen +/- .5 percent when blower comes on may indicate a heat exchanger leak.
dedwards
(Doug Edwards)
June 6, 2010, 4:58pm
4
Im just curious as to where you are taking these flue gas readings?
Additionally, here are some videos of heat exchanger cracks. YouTube…who knew.
The undiluted flue gases. Vent pipe on 80% and 90% furnaces. Up through draft diverter into each cell exhaust.
dredding
(Darin Redding)
June 21, 2010, 4:11pm
6
I’m looking for a recommendation on a combustion gas detector. What devices/brands do you use?
ldapkus
(Linas Dapkus, CMI)
June 21, 2010, 8:19pm
7
dredding
(Darin Redding)
June 21, 2010, 11:30pm
9
Spendy little devices. Wow. And you use them primarily to check o2 and co2 levels at the registers?
I guess my new concern is not discovering a cracked heat exchanger.
ldapkus
(Linas Dapkus, CMI)
June 21, 2010, 11:57pm
11
A good days’ energy audits will pay for the device. I have 3 on hand.