Originally Posted By: kluce
This post was automatically imported from our archived forum.



I ran into a house today where half the house had a basement and the other was a crawl space. The crawl space was insulated under the floor and the interior wall to the basement. Plastic covered the ground. The duct work and water pipes were un-insulated and lastly the extra large door from basement to crawl space was not insulated. There was dampness in the crawl space but no water damage noticed.


I know this is not correct and there are a couple of way to correct this so the crawl space will dry out. But would anyone write this up as a "Major Defect"?

Thanks


Originally Posted By: gbeaumont
This post was automatically imported from our archived forum.



Hi Kevin,


did the crawl space have any ventilation at all, in an ideal world there should be a ventilation openning on each wall and within 3 feet of the corner.

Oh nearly forgot the vent area should equal 1sqft per 150 sqft of floor area.

regards

Gerry


--
Gerry Beaumont
NACHI Education Committee
e-mail : education@nachi.org
NACHI phone 484-429-5466

Inspection Depot Education
gbeaumont@inspectiondepot.com

"Education is a journey, not a destination"

Originally Posted By: kluce
This post was automatically imported from our archived forum.



No ventilation.


It could be a heated crawl space, but the foundation walls are normally insulated and a heat vent installed.


Originally Posted By: rcloyd
This post was automatically imported from our archived forum.



Kevin:


If the under floor area is provided with conditioned air (in addition to the perimeter insulation and vapor barrier already mentioned in your post)there is no need for any ventilation openings through the foundation or outside walls per International Residential Code section 408.2 exception #5.

Regards,


--
Russell G. Cloyd
Intra-Spec Home Inspections
& Code Consulting, LLC
859-586-4591
www.intra-spechomeinspections.com

Originally Posted By: kluce
This post was automatically imported from our archived forum.



At this time it isn’t a conditioned area.


I'm going to write that this can be a "Possible Major Defect" since there is no ventilation or conditioned area.

If anyone can let me know what they think, it would be appreciated.


Originally Posted By: gbeaumont
This post was automatically imported from our archived forum.



Kevin,


If it not conditioned space, I think it needs ventilation, end of story ![icon_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif) ![icon_lol.gif](upload://zEgbBCXRskkCTwEux7Bi20ZySza.gif)

Regards

Gerry


--
Gerry Beaumont
NACHI Education Committee
e-mail : education@nachi.org
NACHI phone 484-429-5466

Inspection Depot Education
gbeaumont@inspectiondepot.com

"Education is a journey, not a destination"

Originally Posted By: kluce
This post was automatically imported from our archived forum.



I agree that correction is needed. But does it fall under the “Major Defect” catigory?


Originally Posted By: ekartal
This post was automatically imported from our archived forum.



I wouldn’t call it a major defect unless you found damp insulation or rot. The need for ventilation depends primarily on the climate.


Erol Kartal
ProInspect


Originally Posted By: gbeaumont
This post was automatically imported from our archived forum.



Hi Kevin,


No I would site it as in need of repair, the repair being the installation of vents, but it is something that I would post to the summaries sheet as well if you use one.

regards

Gerry


--
Gerry Beaumont
NACHI Education Committee
e-mail : education@nachi.org
NACHI phone 484-429-5466

Inspection Depot Education
gbeaumont@inspectiondepot.com

"Education is a journey, not a destination"

Originally Posted By: kmcmahon
This post was automatically imported from our archived forum.



I would guess it would depend on how much work you think is needed to correct it.



Wisconsin Home Inspection, ABC Home Inspection LLC


Search the directory for a Wisconsin Home Inspector

Originally Posted By: kluce
This post was automatically imported from our archived forum.



I understand what is being said, but if you see a number 8 service wire for a 200 amp breaker, even though there is no signs of problems, it still falls under the major defect catigory. In the case of the crawl space, there is no signs of problems but there is dampness and the possibility of future problems could exist. That is why I am questioning. icon_confused.gif


Originally Posted By: rcloyd
This post was automatically imported from our archived forum.



Kevin:


If uncorrected it could cause some major problems. The simple solution would be to install a vent diffuser in the duct that is already within the space. When the Heat, air conditioning or fan runs the moisture you mentioned should go away.


--
Russell G. Cloyd
Intra-Spec Home Inspections
& Code Consulting, LLC
859-586-4591
www.intra-spechomeinspections.com

Originally Posted By: kluce
This post was automatically imported from our archived forum.



That’s what I informed my clients but wrote both options as possible correction.


Originally Posted By: kmcmahon
This post was automatically imported from our archived forum.



There are two categories of major defects IMO.


One would be a major safety hazard that needs attention right now


the other would be a defect or a defect that would take major $$ to correct.


Potential defects are not major...they just have the potential to be. Those that will take little money to correct, but if not taken care of will cost major $$ to repair if left unattended. That's the category I think you are in, and I think you reported it correctly.

This one has nothing to do with your question but I don't believe in potential safety hazards...they either are or aren't. The ones that are, may or may not have surfaced, but are accidents waiting to happen.
Just my .02


--
Wisconsin Home Inspection, ABC Home Inspection LLC

Search the directory for a Wisconsin Home Inspector

Originally Posted By: rcloyd
This post was automatically imported from our archived forum.



Kevin:


If you recommend that they install vents through the outer building wall to outside air their water pipes may freeze and their energy bills will increase substantially. Not recommended.


Regards,


--
Russell G. Cloyd
Intra-Spec Home Inspections
& Code Consulting, LLC
859-586-4591
www.intra-spechomeinspections.com

Originally Posted By: kluce
This post was automatically imported from our archived forum.



I found the “Independent Inspection Addendum” paper that is given to the clients before they order a home inspection.


It's written:

"A "MAJOR DEFECT" is a conditoin that would:
(1) have a significant, adverse effect on the value of the Property; or
(2) significantly impair the health or safety of future occupants of the Property; or
(3) significantly shorten or adversely affect the expended normal life of the Property if not repaired, removed, or replaced.

"MAJOR DEFECTS" are those that could reasonably interfere with Purchaser's intended use or habitability of the Real Estate and are not to be confused with cosmetic defeciencies or maintenance items noted in an inspection report."
Let me know if this is different in your area.