Originally Posted By: srowe This post was automatically imported from our archived forum.
Joe,
where can I get that in black and white…realtor is not so happy with me because electrician says its not a big deal… I know…beyond a home inspection stuff but…I guess I would like to explain.
Originally Posted By: jmyers This post was automatically imported from our archived forum.
Shawn,
What you are looking for is the UL classification, not a breaker specification. You will actually find the classification on the breaker itself in the form of a UL stamp, that it meets the standards for two wires under the termination.
I think it was UL 489, but don't quote me on that.
There are not many breakers that do meet that standard. I know the QO series do, but I can't remember the other ones. If you do a search on our boards for double lugging or double tapping, you will probably find the information in another thread.
Originally Posted By: lkage This post was automatically imported from our archived forum.
jmyers wrote:
Shawn,
There are not many breakers that do meet that standard. I know the QO series do, but I can't remember the other ones. If you do a search on our boards for double lugging or double tapping, you will probably find the information in another thread.
Originally Posted By: jpope This post was automatically imported from our archived forum.
kwilliams wrote:
Jeff, is that a 12 on a 40 amp ??
It appears to be so, but these surge protectors are a bit like A/C condensers in that they will specify the breaker rating to which they are connected regardless of their wire size.
Don't ask me how they work. We don't get much lightning out here, only tornadoes and water spouts.
-- Jeff Pope
JPI Home Inspection Service
"At JPI, we'll help you look better"
(661) 212-0738
Originally Posted By: jmyers This post was automatically imported from our archived forum.
Shawn,
While I don't know who the electrician was, but certainly he would agree that if it was not that big of a deal, there would be no need for the manufacturers to make twin breakers! Or for UL to rate them for one or two wires. They can just start putting as many wires in there that they want. ![icon_cool.gif](upload://oPnLkqdJc33Dyf2uA3TQwRkfhwd.gif)
Think of how much money they could save in breakers if they just started throwing three or four wires under each breaker.
I would be willing to bet the breaker manufacturers won't like that idea!
I would also be willing to bet the NFPA wouldn't be thrilled about it either!
Originally Posted By: Kyle Kubs This post was automatically imported from our archived forum.
Believe it or not this is actually ok the way it is wired… Because it is a “surge suppressor” and the manufacturer specs it that way the smaller gauge wiring is fine. Being double tapped off of the higher amp. breaker where you have two stranded wires that the breaker terminal really can’t tell from one wire is not a problem either… This is a very commonly accepted practice. I don’t write them up. Once I put one in on a separate breaker on a new panel install and the code inspector actually said “most people just put it with the a/c breaker…” Installed double tapped on a 20 amp breaker, that would be different.
– Those that say it cannot be done should stop interupting those of us who are hard at work, doing it…
Originally Posted By: jpope This post was automatically imported from our archived forum.
ekartal wrote:
I believe certain Square D breakers allow for double taps.
Not "double taps," but two wires.
Double tap is a term reserved for use to describe a defect (two wires where only one is allowed). Square D makes breakers that allow for two wires to be properly attached.
-- Jeff Pope
JPI Home Inspection Service
"At JPI, we'll help you look better"