Double tapped main
Originally Posted By: Bob Badger
Mike Parks wrote:
Bob
I strongly disagree. The conductors feeding the "sub" are unfused and are not allowed.
The disconnect 'must' be at the nearest point of entrance to the building.
Using the 1996 230.70(a).
Mike P.
Mike I am sure in your area that is true but the area that this is located in must be like mine and allow exposed service conductors inside the structure.
From the Handbook, opinion not code.![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif)
Quote:
No maximum distance is specified from the point of entrance of service conductors to a readily accessible location for the installation of a service disconnecting means. The authority enforcing this Code has the responsibility for, and is charged with, making the decision as to how far inside the building the service-entrance conductors are allowed to travel to the main disconnecting means. The length of service-entrance conductors should be kept to a minimum inside buildings, because power utilities provide limited overcurrent protection and, in the event of a fault, the service conductors could ignite nearby combustible materials.
Some local jurisdictions have ordinances that allow service-entrance conductors to run within the building up to a specified length to terminate at the disconnecting means. The authority having jurisdiction may permit service conductors to bypass fuel storage tanks or gas meters and the like, permitting the service disconnecting means to be located in a readily accessible location. However, if the authority judges the distance as being excessive, the disconnecting means may be required to be located on the outside of the building or near the building at a readily accessible location that is not necessarily nearest the point of entrance of the conductors. See also 230.6 and Exhibit 230.15 for conductors considered to be outside a building.
The 200 amp service conductors to the original panel are unfused and exposed.
The 100 amp conductors are no different, in the state I live and RI I could do this as long as the panels where side by side, which they are.
Would I do this NO, could I do it is an area that already allows SE cable inside, yes I think so.
I fully understand that some areas do not let an inch of SE in the building, but the 200 amp SE is a give away that this is not one of those areas.
Bob (AKA iwire)
ECN Discussion Forums
Mike Holt Code Forum
Originally Posted By: Dave Nix
Four reasons this would not pass inspection;
Quote:
2002 NEC
110.3
110.14 Electrical Connections.(A) Terminals. Connection of conductors to terminal parts shall ensure a thoroughly good connection without damaging the conductors and shall be made by means of pressure connectors (including set-screw type), solder lugs, or splices to flexible leads. Connection by means of wire-binding screws or studs and nuts that have upturned lugs or the equivalent shall be permitted for 10 AWG or smaller conductors.
Terminals for more than one conductor and terminals used to connect aluminum shall be so identified.
110.22 Identification of Disconnecting Means.
Each disconnecting means shall be legibly marked to indicate its purpose unless located and arranged so the purpose is evident. The marking shall be of sufficient durability to withstand the environment involved.
230.82 Equipment Connected to the Supply Side of Service Disconnect.
Dave Nix
Electrical Matters
Originally Posted By: jpope
Mike, Dave and Bob,
I am grateful for the knowledge and experience you (and a few others) bring to this board. I certainly feel that you are experts in this field even when you disagree ![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif) . When you guys post quote from code books, my eyes get blurry and my head hurts
I previously stated that I felt there needed to be overcurrent protection for the wire feeding the 100A panel. It seems that Mike may agree.
So my question is this;
Will the "average" electrician look at my statement and tell my client that I'm full of schitt?
The double tap is obvious, but how much wire can safely be run without overcurrent protection? It isn't even protected by some type of conduit .
Jeff Pope
JPI Home Inspection Service
(661) 212-0738
Dave I do not agree with your reference to 230.82.
You can have up to six service disconnects and the only possible way to do that is for them to be connected is to the Supply Side of the other service Service Disconnects.
110.22 I can fix with a sharpie. ![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif)
Bob (AKA iwire)
Jeff,
Quote:
There is no overcurrent protection provided for those wires traveling to the "secondary service panel."
I agree 100%
The NEC is a SAFETY code! If it doesn't line-up to code, it isn't safe.
Dave Nix
Electrical Matters
Bob
Very seldom do I think that I beat you. ![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif) This is one of those times.
Please read 230.72(a) 1996. Might be a stretch.
Play ball?
Mike P.
No I do not think any decent electrician will say that the HI is full of it.
Quote:
The double tap is obvious, but how much wire can safely be run without overcurrent protection? It isn't even protected by some type of conduit ![icon_confused.gif](upload://qv5zppiN69qCk2Y6JzaFYhrff8S.gif)
It is up to the local AHJ, in the area I live about 5' or 6' is accepted, in other areas you will not see an inch of service conductor inside the building.
Obviously the less of it the better, and as an HI you should have a pretty good feel for what is 'normal' in your area.
I try to stay with what the NEC says and it is intentionally vague in this area if you believe the NEC handbook.
Bob
Bob (AKA iwire)
Jeff
Use this post. And state that you are differing this to a local pro because there is not a concensus.
Mike P.
Mike of course I will play I even had go and get my 1996 book, it turns out 1996 230-72(a) is the same as 2002
Quote:
230.72 Grouping of Disconnects.
(A) General. The two to six disconnects as permitted in 230.71 shall be grouped. Each disconnect shall be marked to indicate the load served.
Exception: One of the two to six service disconnecting means permitted in 230.71, where used only for a water pump also intended to provide fire protection, shall be permitted to be located remote from the other disconnecting means.
I do not see what your getting at, the marking?
The grouping? these panels look to be 2' or 3' apart I guess you could say they are to far apart.
Respectfully, Bob
Bob (AKA iwire)
Bob
No one ever marks them. ![icon_wink.gif](upload://ssT9V5t45yjlgXqiFRXL04eXtqw.gif)
Jeff
IMHO I believe that the code wanted a main disconnect to the building. This could be six disconnects.
Again IMHO the first panel is feeding the second panel.
If this does not work---Bob--- is the breaker a approved splice?
Mike P.
Originally Posted By: jfarsetta
Okay, so here’s another, though not exactly the same (but kinda close.
400 ampere service to home. Single set of cables from meter pan. Enters home. Gets split in a openable distribution trough. Now, feeds go to separate service panels. Each panel rated for 200 amperes. Each panel wired as a prime. Each panel with a main disconnect. To boot, each panel mounted upside down. Each panel with AJH "approved" inspection sticker.
I may not like it, but I doubt that the configuration needs to be changed, in a real sense. Even the panels being upside down id a no no, but there it was, approved by the electrical inspector...
The feeds were split in the trough.
Joe Farsetta
Illigitimi Non Carborundum
"Dont let the bastards grind you down..."
So engrossed with my own smartness I forgot to look at the second panel.
What about the paralleled conductors? The grounded conductor and the equipment ground are bonded at the second panel. Why did he use a 4 wire to the second panel?
EDIT They may not be bonded. I can not tell if the panel is grounded.
Mike P.
Joe
There must be a disconnect outside or inside before the trough.
Mike P.
Nope… no disco present.
Also, if a disconnect was present, then the panels in question would be wired as subs, with floating neutrals. They were wired as typical main service entry panels.
Again, approved by the AHJ, and in existence since 1984.
So, although this may be poor practice, the question is whether it is permitted. I believe it is.
Joe Farsetta
Hi MIke,
I'm not so sure there would need to be a disco before the trough. I think if the install were set up like "jfarsetta" has described, you would be OK (providing the splices were made properly).
The main problem I see with the install in the photo is the "double tap" on the line side of the main breaker because it is made in an unapproved connection (multiple conductors under one screw). That said, there is most likely a problem with the grounded conductor and the grounding electrode conductor and the main bonding jumper in the secound panel.
Dave Nix
Electrical Matters
Originally Posted By: tallen
Bob,Mike
Is there not a tap rule ? So many feet(18’) maybe without having separate disconnect means as long as the total amperage does not exceed the main disconnect; of course in this case they tapped the main so it does not matter, unless as you stated before it is spliced with split bolt and rubber taped and then double taped at a wrap and a half.What the he** am I talking about icon_wink.gif
I have put the past behind me,
where , however, it now sits, making rude remarks.
www.whiteglovehomeinspections.net
30 Oct 2003-- 29 Nov2005
Here is a composite shot for continuity.
Generally speaking, the "tap rules" apply when smaller sized conductors are tapped from larger conductors and the concern is over current protection.
Dave Nix
Electrical Matters
I did not know the NEC had a generally it either is or it is not. It either meets min code requirements or it does not.A tap is a tap. I guess I will give to the fact that it is a double tapped feeder and is in need of assistance.
Todd,
I was trying not to be too technical.... OK?
Quote:
230.46 Spliced Conductors.
Service-entrance conductors shall be permitted to be spliced or tapped in accordance with 110.14, 300.5(E), 300.13, and 300.15.
As you can see, service entrance conductors have different tap rules than branch or feeder conductors.
Dave Nix
Electrical Matters
Yes ,I know that but they still have to deal with the tap rule and, they cannot be double lugged.OK, I don’t want to fight icon_lol.gif but, sometimes these visual Inspections that we do get way out of hand on this board and it turns into a code thing.