Did a home inspection for an Electrician today and he told me something I never heard before.


I stated to him that the 40 amp LSE is not protected by a breaker at the SE. He told me that it doesn't have to be. Ten Foot Rule states that any LSE that is within 10 feet of a SE does not need to be protected by an individual breaker. It can be tapped.

This is news to me!!!

The LSE was tapped into a live lug just above the main SE breaker. I've been writing these up as "unprotected LSE" since day one.

Someone fill me in, Please.


--
David Valley
MAB Member

Massachusetts Certified Home Inspections
http://www.masscertified.com

"Some cause happiness wherever they go; others, whenever they go."

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



What is an LSE?


There are a few 'tap rules' in the NEC, 10' 25' unlimited etc.

They are handy but many times misused or misunderstood.

Fill me in on the details and I can provide more info.

In general a 'tapped' conductor is protected from overload at the far end instead of the beginning.

In a way service conductors are taps of the utility transformer.


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: dvalley
This post was automatically imported from our archived forum.



Bob,


LSE = Load Side Equipment = Subpanel

OK....Service Entry is protected with a 100 Amp Breaker.

Right above this breaker there are two lug areas that are receiving the neutral and hot from the LSE (Subpanel). Not Protected.

The Sub Panel is adjacent to the SE.

Shouldn't these Sub Panel wires be inserted into a 40 breaker at the SE?


--
David Valley
MAB Member

Massachusetts Certified Home Inspections
http://www.masscertified.com

"Some cause happiness wherever they go; others, whenever they go."

Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



You have described a second service disconnect, not a sub panel, if this was attached to the line side of the “main”.


All service equipment rules would apply.


If he comes off the load side of the main this is a feeder tap.


Originally Posted By: dvalley
This post was automatically imported from our archived forum.



Ah-uh…Got it.


Feeder taps are not allowed, but line side taps are, so long as the second service disconnect is protected by a properly sized breaker.

Thank you Greg.


--
David Valley
MAB Member

Massachusetts Certified Home Inspections
http://www.masscertified.com

"Some cause happiness wherever they go; others, whenever they go."

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



Morning David.


Thanks for clearing up LSE and let me say I think that is a better way to refer to a sub panel.

OK now, feeder taps are allowed as are taps ahead of the main.

I was not out there to see this panel, I am still not sure if I have this correct in my mind.

You have a service panel with a 100 amp breaker, above that breaker are terminals that are being used to feed an adjacent panel.

If I have that right these are indeed feeder taps as they are connected to the load side of the 100 amp breaker

Let me see if I can describe the current path starting at the meter.

Meter > Service Conductors > 100 amp breaker > panel bus > the terminals above the breaker > adjacent panel

If I have this right the lugs above the breaker have 100 amps of OCP (over current protection).

Now some questions.

What size conductors from these terminals to the adjacent panel?

Does this adjacent panel have a main?

What is the adjacent panels rating?

Bob

By the way, I was saddened to hear of your recent lost and I send my sincere condolences. ![icon_cry.gif](upload://r83gSGUzNOacIqpjVReDwcR83xZ.gif)


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: dvalley
This post was automatically imported from our archived forum.



Quote:
What size conductors from these terminals to the adjacent panel?


They were AWG #8

Quote:
Does this adjacent panel have a main?


Absolutely

Quote:
What is the adjacent panels rating?


This particular panel (second Service disconnect) was clearly rated for 60 Amps.

Feedback please......


Thank you for your condolences.


--
David Valley
MAB Member

Massachusetts Certified Home Inspections
http://www.masscertified.com

"Some cause happiness wherever they go; others, whenever they go."

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



OK David it sounds like you may still have violations.


Now I know you are not 'code inspectors' but the easiest to give you the rules for taps is a simple cut and paste job.


Quote:
240.21(B) Feeder Taps

240.21(B)(1) Taps Not Over 3 m (10 ft) Long. Where the length of the tap conductors does not exceed 3 m (10 ft) and the tap conductors comply with all of the following:

(1)The ampacity of the tap conductors is

a.Not less than the combined computed loads on the circuits supplied by the tap conductors, and

b.Not less than the rating of the device supplied by the tap conductors or not less than the rating of the overcurrent-protective device at the termination of the tap conductors.

(2)The tap conductors do not extend beyond the switchboard, panelboard, disconnecting means, or control devices they supply.

(3)Except at the point of connection to the feeder, the tap conductors are enclosed in a raceway, which shall extend from the tap to the enclosure of an enclosed switchboard, panelboard, or control devices, or to the back of an open switchboard.

(4)For field installations where the tap conductors leave the enclosure or vault in which the tap is made, the rating of the overcurrent device on the line side of the tap conductors shall not exceed 10 times the ampacity of the tap


The 8 AWG sounds to small for the 60 amp breaker. {Note 240.21(B)(1)(1)(b) } If the breaker is a 40 or 50 amp (depending on the wiring method used) you are all set here.

If the tap conductors are NM or SE there is a violation of 240.21(B)(1) (3). The tap conductors must be in raceway.

I will be glad to keep bating this around with you here, I will check back soon.

Bob


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: dvalley
This post was automatically imported from our archived forum.



Bob,


I'm referring to the panel itself. It's rated for 60 Amps.

The second service disconnect breaker is 40 Amps.


--
David Valley
MAB Member

Massachusetts Certified Home Inspections
http://www.masscertified.com

"Some cause happiness wherever they go; others, whenever they go."

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



dvalley wrote:
Bob,

I'm referring to the panel itself. It's rated for 60 Amps.

The second service disconnect breaker is 40 Amps.


OK so the 8 AWG is fine with the 40 amp breaker.

Is it cable or raceway?


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: dvalley
This post was automatically imported from our archived forum.



NM



David Valley


MAB Member


Massachusetts Certified Home Inspections
http://www.masscertified.com

"Some cause happiness wherever they go; others, whenever they go."

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



Sorry had to run out and start filling my girls wading pool, it’s gonna be hot one for us today. icon_cool.gif



dvalley wrote:
NM


Then there is a violation



Quote:
(3)Except at the point of connection to the feeder, the tap conductors are enclosed in a raceway, which shall extend from the tap to the enclosure of an enclosed switchboard, panelboard, or control devices, or to the back of an open switchboard


Beyond that the installation sounds OK.

Good luck.


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: dvalley
This post was automatically imported from our archived forum.



Ok, so I’m looking for conduit piping or some sort of protective raceway at any second service disconnect wiring…Right?


Not to include (LSE)sub panels. Right????


Yup, 97 degrees today. My kids have swimming lessons this morning then we're heading to the beach. This is my first Saturday off, since I opened my doors. Strange... because I work every Saturday. Nobody booked for today.


--
David Valley
MAB Member

Massachusetts Certified Home Inspections
http://www.masscertified.com

"Some cause happiness wherever they go; others, whenever they go."

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



dvalley wrote:
OK, so I'm looking for conduit piping or some sort of protective raceway at any second service disconnect wiring...Right?


Correct only in regards to feeder taps, not all LSE is fed with taps.

LSE fed with a standard feeder does not normally require a raceway.


dvalley wrote:
Yup, 97 degrees today. My kids have swimming lessons this morning then we're heading to the beach.


My kids 4 and 6, will start swimming lessons this month. ![icon_cool.gif](upload://oPnLkqdJc33Dyf2uA3TQwRkfhwd.gif)

Have great time at the beach, we usually head to Hampton Beach.


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: jtedesco
This post was automatically imported from our archived forum.



David:


Please post some pictures of this installation here, this sounds very fishy!

The way in which you describe the condition is what is not too clear.


--
Joe Tedesco, NEC Consultant

www.nachi.org/tedescobook.htm

Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



Did we ever establish that this was connected to the load side of the 100a disconnect?


That is the real problem if it is on the line side. You then have an 8 ga NM SERVICE ENTRANCE conductor and the worms start crawling out of the can. We then end up in article 230, not 240 and the real fun begins.


Originally Posted By: bbadger
This post was automatically imported from our archived forum.



Greg Fretwell wrote:
Did we ever establish that this was connected to the load side of the 100a disconnect?
.


Greg I believe so, earlier I posted this description and David did not dispute it.

bbadger wrote:
Meter > Service Conductors > 100 amp breaker > panel bus > the terminals above the breaker > adjacent panel


If this is what he is looking at I see no problem.

If it is a line side tap it may still be OK.


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN

Originally Posted By: bgentry
This post was automatically imported from our archived forum.



I thought that by definition, “line side” is before the mains. correct me if I’m wrong here. So that would mean that if this “path” description is correct, it can’t be line side, but load side rather.


I think what Greg is trying to get accross is that any conductor that is not yet protected is considered SE and falls under those regs. That's why we need to know for sure where this tap is at.


--
Bradley S. Gentry
Superior Home Inspection, LLC
Harrisonburg, Charlottesville, &
Elkton, VA
www.superiorllc.net

Originally Posted By: bgentry
This post was automatically imported from our archived forum.



dvalley wrote:
Right above this breaker there are two lug areas that are receiving the neutral and hot from the LSE (Subpanel). Not Protected.



Ahhh, I think this is our answer.

Greg...does this mean that both panel are to be treated as main panels and panel feeds are both SE?


--
Bradley S. Gentry
Superior Home Inspection, LLC
Harrisonburg, Charlottesville, &
Elkton, VA
www.superiorllc.net

Originally Posted By: bbadger
This post was automatically imported from our archived forum.



Correct line side is before the main.


In this case I believe David has a load side connection and that would make it a sub panel.

If it is a line side connection what you end up with is two service panels which can be done code compliantly also.

It is quite common on large houses to have a 400 amp service feeding two 200 amp panels which are both service panels. Both 200 amp breakers would have to be opened to kill all the power.

The NEC allows up to six service disconnects but they do have to be at one location.


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN