Originally Posted By: berby This post was automatically imported from our archived forum.
Do all electric panel needs a main disconnect? I could not find one in this one.
system
(system)
August 19, 2005, 12:00am
2
Originally Posted By: bkelly1 This post was automatically imported from our archived forum.
no sir.
Was there an exterior disconnect?
system
(system)
August 19, 2005, 12:00am
3
Originally Posted By: lewens This post was automatically imported from our archived forum.
It reverts back to the 6 hand movement rule
– Just my usual 12.5 cents
From The Great White North Eh?
NACHI-CAN
www.aciss-brant.com
www.certifiedadulttrainingservices.com/
system
(system)
August 19, 2005, 12:00am
4
Originally Posted By: berby This post was automatically imported from our archived forum.
There was not a exterior disconnect. Also this panel have about 13 breakers.
system
(system)
August 19, 2005, 12:00am
5
Originally Posted By: aleleika This post was automatically imported from our archived forum.
Was it a condo unit or Townhome?
– A. Dan Leleika
www.a-teamhomeinspections.com
system
(system)
August 19, 2005, 12:00am
6
Originally Posted By: berby This post was automatically imported from our archived forum.
This was a 2700sq. ft. house.
system
(system)
August 19, 2005, 12:00am
7
Originally Posted By: Greg Fretwell This post was automatically imported from our archived forum.
The right way to ask the question is
“was there an overcurrent device feeding this panel”
That could be the main disconnect outside or this could be fed from another panel with a breaker in it. Within some specific 240.21(B) rules this could be fed directly from the load side of the service disconnect but usually a feeder will have a breaker where it leaves the serving panel.
If this is a sub panel in the same building the “six switch” rule does not apply.
system
(system)
August 19, 2005, 12:00am
8
Originally Posted By: berby This post was automatically imported from our archived forum.
Don’t read to much into this question. The power come out of the ground then into the meter then into this panel. This is the only panel.
system
(system)
August 19, 2005, 12:00am
9
Originally Posted By: Greg Fretwell This post was automatically imported from our archived forum.
If there is no disconnect in the meter can you have a violation.
The only caveat is if there is a disconnect somewhere on the property you may still have a legal installation.
system
(system)
August 19, 2005, 12:00am
10
Originally Posted By: ekartal3 This post was automatically imported from our archived forum.
13 breakers yes, but don’t double-pole count as one in the six throw thing?
Erol Kartal