No main disconnect on todays inspection

Hello, I was inspecting a home today and on the electrical panel I did not see a MAIN disconnect. I need to know if I am missing something here and would it require me to refer this to an electrician? I also have some plugs that are not showing a ground. any an all help would be greatly appreciated.

The box on top is the breaker box in the home. thanks for your help.

Where was the location of the meter?

1 Like

on the side of the house. here is another pic.

Also have this.

The cabinet below the meter is probably the service disconnect, Stacey.

Did you open it?

3 Likes

yes it is the bottom picture of the first set of pictures I started with. just has 20 and 30 amp breakers.

I think that the conduit from the meter is feeding the one in the house. your thoughts?

What the frock is that??? :flushed:

5 Likes

Handy mans best. heck you would think you at least put it into the wall to hide it.

To much going on. Refer it on in simple terms.

1 Like

Ya, what is that simple term!!!

to quote the tenant this place ________

You have a mess that’s for sure. One panel’s wired like a main, and one is wired like a sub. But it looks like the wrong one is wired like a sub.
And of course as you’ve already noted no disconnect, at least not in those photos.

1 Like

So the way I see it refer it to an electrician. if we are suppose to turn electricity off in 6 steps, they have to do the inside and then go outside to complete. Am I wrong?

They are probably using the 6 throw rule for the service disconnect but that system has some problems e.g. ungrounded wire on neutral/ground buss, neutral wire un marked on breaker, upside down breakers (on when in down position, double lugged wires on termination for 1 wire, etc., etc.

I would refer it out to a qualified electrician to make corrections, as needed, for a safe usable system.

2 Likes

This should be referred to an licensed electrician? not a electrical contractor. please help.

Thank you all for your help. I do APPRECIATE IT.

1 Like

This is how I used to refer them out. If he screwed the pooch, he was not qualified.

2 Likes

Holy fire risk batman LOL

2 Likes