smayhan2
(Shane Mayhan, TREC 22021)
January 24, 2018, 3:36pm
#1
Can anyone tell me where in the IRC it states that an electric water heater must be elevated 18" in a garage?
jfunderburk
(Joe Funderburk, CMI)
January 24, 2018, 3:38pm
#2
It doesn’t. “Ignition source” must be elevated 18".
cevans
(Chuck Evans, CMI)
January 24, 2018, 3:39pm
#3
The ignition source must be 18 inches above the floor. When you read the definition for ignition source it becomes clear that the contacts in the electric water heater are a source of ignition.
Per IRC R202
For my home installation, I needed to raise the unit about 8 inches to get the ignition source above 18 inches.
M1307.3 Elevation of ignition source. Appliances having an
ignition source shall be elevated such that the source of ignition
is not less than 18 inches (457 mm) above the floor in garages.
For the purpose of this section, rooms or spaces that are not part
of the living space of a dwelling unit and that communicate
with a private garage through openings shall be considered to
be part of the garage.
For gas appliances
G2408.2 (305.3) Elevation of ignition source. Equipment and
appliances having an ignition source shall be elevated such that
the source of ignition is not less than 18 inches (457 mm) above
the floor in hazardous locations and public garages, private
garages, repair garages, motor fuel-dispensing facilities and
parking garages. For the purpose of this section, rooms or
spaces that are not part of the living space of a dwelling unit and
that communicate directly with a private garage through openings
shall be considered to be part of the private garage.
Water heater specific, regardless of fuel
smayhan2
#4
Thank you, would you have the reference?
smayhan2
January 24, 2018, 3:43pm
#5
That answered my question, thank you for your help.