Originally Posted By: jpeck
This post was automatically imported from our archived forum.
Robert is at a disadvantage (without his books) hence his incorrect numbers.
First, lets start here.
ARTICLE 240 Overcurrent Protection
-240.24 Location in or on Premises.
- - (A) Accessibility. Overcurrent devices shall be readily accessible unless one of the following applies: (itemizations not included)
- - (B) Occupancy. Each occupant shall have ready access to all overcurrent devices protecting the conductors supplying that occupancy. (exceptions do not apply here, so they are not included)
- - - [Jerry's note: Being in a bedroom does not make them accessible to all occupants. Sometimes this gets fuzzy with the AHJ, but have them think about it a while and they should realize that a locked bedroom door is intended to exclude everyone except the occupants of the bedroom.]
- - (C) Not Exposed to Physical Damage. Overcurrent devices shall be located where they will not be exposed to physical damage.
FPN: See 110.11, Deteriorating Agents.
- - (D) Not in Vicinity of Easily Ignitible Material. Overcurrent devices shall not be located in the vicinity of easily ignitible material, such as in clothes closets.
- - - [Jerry's note: This does not say "cannot be located in clothes closets", it says "such as" clothes closets, and that bedroom sure does fit that inclusion.]
- - (E) Not Located in Bathrooms. In dwelling units and guest rooms of hotels and motels, overcurrent devices, other than supplementary overcurrent protection, shall not be located in bathrooms as defined in Article 100.
ARTICLE 240(B) and (D) apply to that photo.
Now, for clearances (you already said you knew - good).
The working space must be 30" wide (which does not mean 30" on each side or even centered on the panel) by 36" in front of the panel. And it must be from the floor to the height of the equipment (at its top).
110.26 Spaces About Electrical Equipment.
- (A) Working Space.
- - 3) Height of Working Space. The work space shall be clear and extend from the grade, floor, or platform to the height required by 110.26(E). Within the height requirements of this section, other equipment that is associated with the electrical installation and is located above or below the electrical equipment shall be permitted to extend not more than 150 mm (6 in.) beyond the front of the electrical equipment.
- [Jerry's note: it said to go to (E), so here it is.] (E) Headroom. The minimum headroom of working spaces about service equipment, switchboards, panelboards, or motor control centers shall be 2.0 m (6? ft). Where the electrical equipment exceeds 2.0 m (6? ft) in height, the minimum headroom shall not be less than the height of the equipment.
Exception: In existing dwelling units, service equipment or panelboards that do not exceed 200 amperes shall be permitted in spaces where the headroom is less than 2.0 m (6? ft)
- - - [Jerry's note: 6' 6" does not apply to dwelling units if under 200 amp, and that looks under 200 amp. In this case, you would use "the minimum headroom shall not be less than the height of the equipment"]
- (B) Clear Spaces. Working space required by this section shall not be used for storage. When normally enclosed live parts are exposed for inspection or servicing, the working space, if in a passageway or general open space, shall be suitably guarded.
[Jerry's note: Clear space? Means no bed in that required working space. But, you can move the bed, right? Of course, it's easy. But no one is going to say that the bed can be in the working space, are they? Then when excuse a car parked in the garage and parked in the working space? Just raising the question again, if the car is not a problem the bed is not a problem. I think they are both problems.]
Enough for now. Get too long and I lose track of where I'm going and you lose track of where I've been.
--
Jerry Peck