Electrical Panel - Infrared Scan
To start with, that camera is a hobby camera. Turn off the MSX and see if you can identify anything by the palette colors. It’s a big blob. Actually, look closely, you will see that the MSX does not align with the colors.
Electrical IR is the easiest application you can do with IR. But you can’t be looking for Quantitative data as a “go/no go” with that camera. You also are not analyzing the target for how hot it is based on AI data. You need to know what is causing heat and why. Likewise, you not only need to know IR, you need to know everything about what you’re pointing it at, and know what you expect to see when you do. Only 1% of the time are you going to find the device about to melt down as being the problem. What causes the heat? Loose wire connection, loose breaker connection to the buss, defective internal components or the breaker, excessive load, a reflection… With training, you will learn through quantitative observation what each of these are. Then you can go find the problem.
If you see something hot, you need to put down the camera and start looking for the source of the heat. What is the amperage on the circuit. Is it at full load or not. A 20 amp breaker does not run at 20 amps hardly ever. 5 amps can make a lot of heat. What will the temperature be if you up the load to 15 amps? Don’t ever try that!
The temperature you are getting with the camera is an indirect measurement in most cases. Things cool down based on mass, density, conductivity, ambient conditions etc. You will miss the 2,000F Arc where the breaker connects to the buss when it is only 80F by the time it gets to the surface.
The problems go on. The best you can hope for is to use that camera like a glorified flashlight. If you see something in IR, go find out if is anything through normal HI Inspection Standards. Then report it, without putting IR in the report. Unless you can explain psychrometric and thermodynamic reasons for your findings while sitting in a courtroom, don’t do it.
If you can’t afford a couple of thousand dollars on training and get rid of that $400 camera, stick to using it like a glorified flashlight. The course you took qualifies you to turn the camera on and how it works. The camera has no idea what the potential issues are. It just assigns a color for how you adjust the camera, and I bet you did not adjust your camera, right? If not, don’t use the numbers. IR can make things look like a forest fire at a .1 degree differential. They are an apparent temperature and are never correct unless you tune the camera for one target in the scan. These are not a photograph. It is a spreadsheet. Colors are assigned for range and span. You can have a problem hidden in that red spot if you use the wrong settings and color span.
David,
I don’t do IR but I’m curious is there some sort of calculation that you would use to determine if the temperature of the breaker is normal or abnormal based on the load?
Hi David,
Thanks for your input and your response. I think this helped me to understand to use my eyes more than the camera and to stick to looking for signs of scorching, melting or loose connections. I think sticking to the SOP will help simplify the process. The technology is cool but complicated. The camera has an automatic mode and manual mode. You can adjust the pallete, temperature range, emissivity among other things. I really have not put a lot of time into trying to dial it in and shouldnt have posted the photos I took. Still a lot to learn, but I think it can be easy to get wrapped into things that are out of my knowledge realm simply out of curiosity. Thanks!
How could that work? The thermal trip rating of a breaker is defined by the breaker’s ampere rating, which indicates the maximum continuous current it can carry without tripping. Didn’t David just indicate that the internal temperature of the breaker will be different than the external temperature seen by an IR camera. Different breakers with different construction are each going to have a dfferent thermal signature not one that can be calculated by a simple formula.
I’m sorry, I was meaning to add that. :unamused_face:
Yes, there is a calculation that can determine an apparent temperature rise if load is increased to capacity. We can look at the equipment on the circuit, or just add a factor based on max load and considering inductive and resistance load expected.
This is an apparent result because, as we talked about, camera adjustment is critical if the temperature result needed is critical. Putting the inaccurate data into the calculation is going to get worse. However, it really shows how bad it will get if we have a hot device with a low load. Temp rise is not linear so we can’t just use a % rise.
We use this as a spreadsheet, so there are a lot of factors involved. Not simple algebra.
Post anything you want here! Experience plays a major factor in analyzing IR Scans. You won’t get this out of a book because this stuff is constantly changing from outside sources. We can give direction in the direction to head. You’re there, we are not, so you need to know what data you need to collect and consider as necessary. What it is, and why it is, does not come out of the camera.
Thanks for the detailed response. I’ve dealt with questions about IR scans in HI and other reports stating that a certain circuit breaker is too hot or something similar. My first question is always what was the load on the circuit breaker and in almost every instance no load measurement was taken.
Yes, thank you for pointing that out. Hope my previous reply addresses that also. The point you’re making is correct when we try to get an absolute measurement. Most of the time in the field, “close” is close enough. The electricians I work with take those big assed panel covers off, and take amperage readings, so I can keep out of the blast zone, generally just yank the part out, replace it so we can come back before we are done to confirm. Laboratory analysis can be done, but generally not needed.
It is a great tool to be able to determine on site if it is going to go bang or something to address during maintenance schedules.
They love to take moisture measurements when they see the color Blue!
IR does not detect moisture, neither does a moisture meter. An amperage reading does determine load, which has a direct bearing in heat amount associated with voltage, amperage and resistance. Though not 100%, determining apparent temperature rise calculation is an important practice to consider.
At some point, the IR may detect a temperature above something like conductor insulation ratings, but that is higher than almost all “How hot is too hot”? Not very often…