Originally Posted By: hgordon This post was automatically imported from our archived forum.
This was at the Svc Disc of a Package AC Sys
system
(system)
May 22, 2004, 12:00am
2
Originally Posted By: hgordon This post was automatically imported from our archived forum.
Im in the middle of sriting this report. What type of a breaker is this?
system
(system)
May 22, 2004, 12:00am
3
Originally Posted By: tallen This post was automatically imported from our archived forum.
Best I can say from the pic it is a double poll 60 siemens . Hopefully Joe Tedesco will show up.
You should PM him .
-- I have put the past behind me,
where , however, it now sits, making rude remarks.
www.whiteglovehomeinspections.net
30 Oct 2003-- 29 Nov2005
system
(system)
May 23, 2004, 12:00am
4
Originally Posted By: jtedesco This post was automatically imported from our archived forum.
A non automatic circuit breaker is a switch, and will be better understood if you do a search on Google for a “non automatic circuit breaker”
– Joe Tedesco, NEC Consultant
www.nachi.org/tedescobook.htm
system
(system)
May 23, 2004, 12:00am
5
Originally Posted By: jtedesco This post was automatically imported from our archived forum.
Quote:
Non-automatic circuit breaker ? A circuit breaker which has no automatic thermal overload trip
element but does have a magnetic trip element for short-circuit/fault protection. Short-circuit and overload
protection must be provided by an upstream overcurrent device.
-- Joe Tedesco, NEC Consultant
www.nachi.org/tedescobook.htm
system
(system)
May 23, 2004, 12:00am
6
Originally Posted By: jtedesco This post was automatically imported from our archived forum.
Deleted duplicate
– Joe Tedesco, NEC Consultant
www.nachi.org/tedescobook.htm
system
(system)
May 23, 2004, 12:00am
7
Originally Posted By: hgordon This post was automatically imported from our archived forum.
Yeah Joe…but what does that mean to my client?
system
(system)
May 23, 2004, 12:00am
8
Originally Posted By: jtedesco This post was automatically imported from our archived forum.
Gordon:
I believe that the second sentence in the definition help us to understand: "Short-circuit and overload protection must be provided by an upstream overcurrent device." This means that there must be another overcurrect device ahead of this circuit
-- Joe Tedesco, NEC Consultant
www.nachi.org/tedescobook.htm
system
(system)
May 23, 2004, 12:00am
9
Originally Posted By: tallen This post was automatically imported from our archived forum.
I have never came across one of those . Thanks Joe
– I have put the past behind me,
where , however, it now sits, making rude remarks.
www.whiteglovehomeinspections.net
30 Oct 2003-- 29 Nov2005
system
(system)
May 23, 2004, 12:00am
10
Originally Posted By: hgordon This post was automatically imported from our archived forum.
So heres my question…what good is it, other than to shut off service to the unit?
And to make matters worse, look what's upstream:

system
(system)
May 23, 2004, 12:00am
11
Originally Posted By: tallen This post was automatically imported from our archived forum.
I say it is simple.
Recommend a licensed Sparky and go on your way.
Wait are you saying that 60 is the main for that panel????
Does not matter report is the same Sparkey!
-- I have put the past behind me,
where , however, it now sits, making rude remarks.
www.whiteglovehomeinspections.net
30 Oct 2003-- 29 Nov2005
system
(system)
May 23, 2004, 12:00am
12
Originally Posted By: jtedesco This post was automatically imported from our archived forum.
Quote:
This was at the Svc Disc of a Package AC Sys
I didn't see this until now.
The disconnecting means at the AC unit will satisfy the ready access to it, but now I smell a fish!
First thing is to look at the label on the unit to see what it says related to: "Maximum Fuse Size" or "Maximum Fuse Size or HACR Circuit Breaker"
The panelboard that you show, does it have an overcurrent device that is used to protect the branch circuit to the unit?
If so I would check to see if it is a HACR CB like I mentioned above if on the label.
Otherwise it is a HOT POTATO and you should do the typical recommendation to cover your a$% .
-- Joe Tedesco, NEC Consultant
www.nachi.org/tedescobook.htm
system
(system)
May 23, 2004, 12:00am
13
Originally Posted By: hgordon This post was automatically imported from our archived forum.
Joe, Mfg Recommended Max CB is 40Amps
system
(system)
May 23, 2004, 12:00am
14
Originally Posted By: hgordon This post was automatically imported from our archived forum.
Do I state Over Fusing AT Svc Disc taking into consideration now the issue of the Non-automatic circuit breaker?
system
(system)
May 23, 2004, 12:00am
15
Originally Posted By: tallen This post was automatically imported from our archived forum.
– I have put the past behind me,
where , however, it now sits, making rude remarks.
www.whiteglovehomeinspections.net
30 Oct 2003-- 29 Nov2005
system
(system)
May 23, 2004, 12:00am
16
Originally Posted By: tallen This post was automatically imported from our archived forum.
A/C disconnect is over fused recommend evaluation by a licensed electrician before the close of escrow.
– I have put the past behind me,
where , however, it now sits, making rude remarks.
www.whiteglovehomeinspections.net
30 Oct 2003-- 29 Nov2005
system
(system)
May 23, 2004, 12:00am
17
Originally Posted By: roconnor This post was automatically imported from our archived forum.
Harvey,
If I understand you correctly that 60A switch is at the unit, which is not over-fused and doesn't need to be an auto breaker since it is just being used to shut off power to the unit for servicing (disconnect or lock-out required by model codes). Then there should be a 40A max standard breaker at the panel to protect the wires and unit. If that is the case I don't see a problem.
But that looks like an FPE panel, which I think is an automatic flag for further evaluation by a licensed professional.
Hope that helps ... 
-- Robert O'Connor, PE
Eagle Engineering ?
Eagle Eye Inspections ?
NACHI Education Committee
I am absolutely amazed sometimes by how much thought goes into doing things wrong
system
(system)
May 23, 2004, 12:00am
18
Originally Posted By: jpeck This post was automatically imported from our archived forum.
Harvey,
That is simply a molded case switch, just like putting in a non-fused pull out disconnect.
It offers no overcurrent protection and is there to serve only as a means of disconnect for serving the unit.
Like putting in a real heavy duty rated double pole switch (actually, not "like" that, that "is" what that is, a 60 amp rated double pole switch).
-- Jerry Peck
South Florida
system
(system)
May 23, 2004, 12:00am
19
Originally Posted By: tallen This post was automatically imported from our archived forum.
– I have put the past behind me,
where , however, it now sits, making rude remarks.
www.whiteglovehomeinspections.net
30 Oct 2003-- 29 Nov2005
system
(system)
May 23, 2004, 12:00am
20
Originally Posted By: roconnor This post was automatically imported from our archived forum.
Jerry … no comment about the FPE panel …
– Robert O’Connor, PE
Eagle Engineering ?
Eagle Eye Inspections ?
NACHI Education Committee
I am absolutely amazed sometimes by how much thought goes into doing things wrong