I’ve been asleep for 8 years: so you don’t have to be. Sediment trap

So I finally did go past the code check book, and look up the actual regulations. Lo and behold. It turns out the diagram used was right for the wrong reason. The code changed twice:

2013 CPC Section 1212.8 Sediment Trap
Where a sediment trap is not incorporated as a part of the appliance, a sediment trap shall be installed downstream of the appliance shutoff valve as close to the inlet of the appliance as practical at the time of appliance installation.

2016 CPC Section 1212.8 Sediment Trap
Where a sediment trap is not incorporated as a part of the appliance, a sediment trap shall be installed downstream of the appliance shutoff valve as close to the inlet of the appliance as practical, before the flex connector, where used at the time of appliance installation.

2019 CPC Section 1212.9 Sediment Trap
Where a sediment trap is not incorporated as a part of the appliance, a sediment trap shall be installed downstream of the appliance shutoff valve as close to the inlet of the appliance as practical, before the flex connector, where used at the time of appliance installation.

2022 CPC Section 1212.9 Sediment Trap
Where a sediment trap is not incorporated as a part of the appliance, a sediment trap shall be installed downstream of the appliance shutoff valve as close to the inlet of the appliance as practical at the time of appliance installation.


That said +1 to " If the “guy” doing the works needs your schematic to do it right, he’s the wrong guy (I’ve said that so many times to agents calling me to ask about my report it’s not even funny)." from @mfellman

4 Likes

You can use galvanized pipe, copper pipe or black pipe for gas. But black pipe is cheaper and the preferred material. Some people don’t know what they are doing, so just to identify the type of supply line it is, it’s best to keep it simple and standard. Hell I have never seen a copper gas supply, and who knows maybe it’s code compliant to use PEX for gas, but should we?

Fun read from an old thread:

I’ve seen a few copper supply installs on propane systems… usually, in a rural area far off the gas grid. I remember a rule/code, etc. about labeling the piping if other than black iron in areas outside of where the appliance that is serves is located. Basically, Joe the plumber should be smart enough to not assume a copper pipe holds water if the furnace it’s serving is in the same room.

I’ve only seen copper gas line once. It has to be Type K. This line did not have any markings, so I wrote it up as “No evidence that copper pipe is rated for use as a gas pipe.”

2 Likes