Overheating is definitely a cause for concern here. NEC Table 310.15(B)(2)(a) shows derating of conductors when there is more than 3 in a raceway. A 12 awg. copper THHN insulation copper conductor is good for 25 amps with not more than 3 wires in the raceway. When a raceway exceeds 20 wires it needs to be derated to 45% of 25, or 11.25 amps. Taking it one step farther if the number of conductors exceed 40, it derates to 35% or 8.75 amps. All of this derating is to allow for cooling of the conductors. I’d take a real close look at the whole electrical system. When I was wiring houses we were told if nothing else, make the panel look good, most inspectors will stop looking further if it looks good.