Inspection today on a Manufactured Housing 1994 and found this type of Electrical panel I never seen before.
Appears to have been manufactured by Square D which is common around here.
The whole panel, tub and panel front is all plastic.
Found three neutral conductors that are overheated at on time and not sure what caused it.
Two possible causes for the neutral over heating .
Most common is the fastening screw Not tightened properly at instillation .
The other is the neutral is the return for two hot wires .
Thanks guys, this was very helpful.
The post from Paul back in 2007 helped.
Never come across such a thing before and done many trailers.
Panel cover comes off hard. A breaker 20 for that panel is $55 I just found.
The home is been vacant for 2 years. The owner was there during the inspection doing outside work.
You might have noticed that there is no main breaker.
It is being fed from a 200 amp panel GE in the detached garage.
I deferred to to an electrician, but the clients Father is a Master Electrician.
He also had made a comment to his that he had never seen these type panels.
No problem with that, since this is the service equipment. However, I do not see where the terminal bar is bonded to the enclosure. Were you able to verify the bond?
Those Trillaint panels were an attempt by Sq D to come up with a new way of installing services/sub-panels solely with NM cable and an entirely plastic enclosure. They never really caught on but I can remember a big display they had set up in the supply house in the 90’s.
If this is in a separate structure then a disconnecting means and a GES is required. What is the unit that the feeder conductors are attached to?
The CB at the bottom of your photo should be the disconnecting means. There is a separate EGC and the neutrals and EGC’s appear to be separate. As long as there is a grounding electrode system you should be OK once the burnt conductors are repaired.
Thanks Robert and I just noticed, there are four conductors leaving the main panel and only 3 entering the trailer panel.
Wonder what happened to the fourth one.?
Woops
looks like some one is trying to convince all they have two hots a neutral and a ground . Not good .There should be only one ground in the system … Roy
From what I can see you have 4 conductors on both ends of the feeder. The service panel should have only 3 conductors feeding it which appears to be at the bottom left of this photo.