Is inadequate roof or attic ventilation a defect?

Brian,

Unless that Certainteed Warranty item you posted has been updated since I last viewed the limitations, I believe that the warranty length is reduced to a total of only 10 years, regardless of which Certainteed Roofing Shingle or Shangle was applied under the circumstances referenced to.

Regarding your most recent post response, how could moisture jump from one enclosed rafter bay to all of the others, even if there had been a bathroom exhaust vent releasing its moisture directly into the attic.

In reality, there was no attic area, becaust this was a vaulted/cathedral ceiling structure for the entire home.

Ed

Not all, Ed

[size=4]Inadequately Ventilated and Non-Ventilated Decks[/size]

[size=2]Any shingles applied to inadequately ventilated or non-ventilated decks, other than the shingles and deck systems described in the paragraph below, titled “Insulated Decks and Radiant Barriers,” shall qualify for a reduced warranty duration of 10 years with no SureStart coverage, with respect to shingle problems related to the absence of adequate roof system ventilation.

[/size][size=4]Insulated Decks and Radiant Barriers
[/size]

[size=2]CertainTeed’s Limited Asphalt Shingle Warranty, including SureStart [/size]™ coverage, will remain in force when its fiber glass asphalt shingles manufactured to meet ASTM D3462 are applied to roof deck assemblies (slopes ³ 2:12) where foam insulation is prefabricated into the roof deck system (often called “nailboard insulation”), where insulation is installed beneath an acceptable roof deck system, or where radiant barriers are installed, [FONT=Garamond-BookCondensed]with or without ventilation directly below the deck. Acceptable roof deck surfaces must consist of either minimum [/FONT]3/8" thick plywood or minimum 7/16" thick OSB. If an alternate deck surface material is being considered, contact CertainTeed Technical Services.

See the following important restrictions.
The design professional is responsible for ensuring

  1. proper quality and application of the insulation and/or radiant barrier,
  2. provision of adequate structural ventilation and/or vapor retarders as determined to be necessary, and
  3. that all local codes are met (particularly taking into account local climate conditions). Special attention must be taken if cellular foam, fiber glass, or cellulose insulations, or other highly-permeable insulation will be used in an unventilated system, or if the insulation/rafter or insulation/joist planes may create an air leak that could lead to moisture transmission and condensation problems.

*All these important factors and decisions, while **not *[size=2]the responsibility of CertainTeed Corporation, are critical to assure proper deck system performance.[/size]

My comments:

  1. what is “structural ventilation”? Never heard of this before; someone’s making up new terms!

  2. the highlighted text in the last paragraph of the warranty restrictions is essntially telling people to not use the attic/roof cavities as a means to ventilate the house. This concept goes back the the 1940-50’s. A bit of history from a 1986 Building Science Insight CE session (1 day; $250) I attended:

Consequences of an Ineffective Air Barrier System
The concept of the building envelope as an environmental separator was first promoted by Dr. Neil Hutcheon, former Director of the Division of Building Research, in a talk to the Engineering Institute of Canada in 1953.¹ Dr. Hutcheon listed the principal requirements of the building envelope, so that each could be addressed separately and in conjunction with its counterparts. He noted that building envelops had to be designed to control air flow and the moisture and energy flow associated with it. To quote from his talk:
“The flow of heat, moisture and air in walls have implications not only by themselves, but for all the other considerations listed. **Air merits major consideration mainly because of its influence on heat and moisture flow.”**Remember, this is 1953 (hell, I was only 3 then), more than a 1/2 century ago! How smart are we really to not listen to or respect those that have much deeper insights into what is really happening in buildings???

Utah does not have a “code” for proper attic ventilation. I have called out "no ventilation many times and still do. But it is per the shingle manufacturers request to honor a warranty on their shingles that has min. ventilation req. Just look on a package of shingles.

Here’s where the interesting stuff begins:

In a June, 1994 Energy Design Update article Building Scientists Turning Code and Common Practices Upside Down:
“At the ASHRAE / DOE / BETEC* Thermal Envelopes Conference* in Clearwater, Florida, an international group of building scientists and contractors led by Anne Silberstein of Isover Saint-Gobain of France and Bill Rose of the University of Illinois Building Research Council concluded that unvented cathedral ceilings provide better thermal performance and better moisture protection than conventional vented cathedral ceilings”

Isover Saint-Gobain owns Certainteed!!! Why would a shingle company say this??? Maybe they know something many don’t. They offer a full warranty on some of their products installed without venting!

In the August, 1998, Journal of Light Construction, Bill Rose in the Q&A section states:
“We’ve also found that a vented cathedral ceiling cavity is much hotter than an unvented full attic, other things being equal”

So the unvented full attic is cooler than the vented cathedral!! Why would we want to vent it to save the shingles from heat? It’s already cooler. As I’ve said earlier, vented cathedral ceiling shingles should be failing much faster and more frequently than the unvented full attics since they are hotter.

"So far I find little technical support for the claim that ventilation enhances the service life of shingles. … the temperature difference between vented and unvented is awfully tiny. Shingle colour and latitude make for a much greater temperature difference. In the absence of technical support, I believe that either course of action- venting or not venting- is viable. Those who vent will encounter fewer problems with code officials and shingles warranties. Those who do not are working in the fine tradition of craftspersons who use common sense to challenge accepted wisdom.
Venting has been presented as the key to blissful service life of shingles.

My opinion is that service life is first and foremost a matter of shingle quality. If** ventilation has one ill effect**. it is that it gives shelter to manufacturers who are not investing in shingle improvement."
**
**Why do the shingle companies not publish some actual shingle roof temps from their own studies with the main variables- latitude, orientation, shingle colour and venting- studied. They are huge and have more money than any little university research group!!

I think me smells the truth being ignored or buried!!!

Brian,

There is much more to the situation than just temperatures. Even in one of your favorite researchers view points, from Joseph Lstiburek, he points out the decrease in a 15 year shingle roof, (How old is this document?), will be about 3-4 years.

The rational for the unvented assembly is to promote higher quality internal health, thereby reducing mold and other moisture related occurrences.

Please review the following link. It is not dated, so I don’t know what era this research paper is from.

Ed

http://64.233.167.104/search?q=cache:kcPfF4acwpAJ:www.noblackmold.com/news_files/UnventedAtticsArticle.doc+prblems+with+unvented+shingle+roofs&hl=en&ct=clnk&cd=2&gl=us

Excerpted paragraph from the above paper:

Unventing roof assemblies in most climates increases the air conditioning load on a typical home by approximately 3-to-5 percent. If the ducts are inside the conditioned space and we are not worrying about mold, humidity, ice-damming or blowing snow issues, vent the roof and don’t give up the 3-to-5 percent.

Remember there is a trade-off. I choose to give up the 3-to-4 years in the life of my shingles **(ed; out of a 15 year shingle warranty. That is a loss of 20% to 27% of the expectet shingle life.), **in exchange for better performance for the entire system and I choose to void the warranty. Not all people will want to make this choice. I already see their logic. Yes, I prefer mold in my house in Orlando, FL in exchange for 3-to-4 years more on my shingle life; and yes, I want my shingle to be black or brown in Austin, TX so that I can install a 1-to-2 ton larger air conditioner.

**Is this some of the logic and rationale that I would like to emmulate and follow? **

Ed

Some More From That Paper:

Now, where the real effect of not venting roof assemblies is felt is the temperature of the underside of the roof sheathing. My field measurements and compute modeling show that the temperature of the underside of the roof sheathing increases between 10 and 20 degrees F. Why the huge difference here and not on the shingles? Well, compare the R-value of a shingle and the R-value of the roof plywood. A temperature gradient can actually exist across the plywood. And, ventilation air on the underside of the roof plywood does remove heat. Take away the ventilation air and you do increase the temperature of the underside of the plywood. But does this matter? Yes and no. Depends on the overall system design.

Unventing roof assemblies in most climates increases the air conditioning load on a typical home by approximately 3-to-5 percent. If the ducts are inside the conditioned space and we are not worrying about mold, humidity, ice-damming or blowing snow issues, vent the roof and don’t give up the 3-to-5 percent.

But if you are stupid enough to put ducts in attics, if you are stupid enough to put air handlers in attics, if you are stupid enough to hire interior designers and architects that design incredibly complicated roof structures that cannot be air sealed at the interior drywall because of jigs, jogs, shelves, coffers, pot lights, valleys, hips, dormers, beams, skylights, etc., give up the 3-to-5 percent. Guess what you gain? You gain between 10-to-30 percent savings from the airtightness of the roof sheathing and lack of conductive gain on ductwork in vented attics.

Proper soffit to ridge ventilation does decrease moisture content, especially that which has migrated into the deck sheathing.

Brian,

Please read page 10 of the following link.

Ed

http://txspace.tamu.edu/bitstream/1969.1/4545/1/ESL-HH-06-07-34.pdf

Interesting advice from a fellow member:

Other cladding problems may be specific to certain regions. Brian MacNeish, a partner in Atlantic Home Inspections of Sackville, New Brunswick, often sees buckled Masonite hardboard siding on houses built in the Maritimes after 1960. There, the cause of the problem is moisture forcing its way out of the house, not in. “The houses have no ventilation,” MacNeish explains, “so moisture inside gets through the aspenite or clipboard sheathing and into the hardboard. We usually recommend adding vents.

And from the other partner author of this report:

Predictably, we are also finding peeling paint and much wood on several upper-level window sills. We know by now that this is evidence of water seeping in. The solution lies in sealing the windows from the outside and repairing the spalled brick. Had we seen no flaws in the shell of the house, we would have suspected the damage was cause by moisture trying to get out- in other words, an elevated humidity level in a tightly sealed house. In that case, Dunlop suggests putting vents in the roof and/or soffits under the eaves, not too costly a job. A dehumidifier might help too.

If Mr.Dunlop wants to recommend attic ventilation for interior house moisture problems, that’s his issue. (if you notice I have essentially been saying: “Don’t vent the house through the attic; airseal for moisture and energy reasons and install interior exhaust fans”). A humidifier will only bring the interior moisture levels down to 50% RH or so, still way to high to prevent window and potential hidden wall/attic condensation in cold winter temps. We use dehumidifiers here for controlling summer humidities in basements and to help dehumidify after serious water spills/leakage (along with massive house ventilation and heat)

Brian,

Since the article was not dated when I was doing my research, I had fugured that it was from some time ago. I know you have a firm stance regarding this topic and it did not seem to jive with your current views.

Did you happen to have time to review my previous back to back posts, excerpted comments, and the linkds they came from yet?

My trouble with your stance is that I have seen the structural devestation on deck sheathing from inadequate ventilation. Although the roof surface temperatures may likely be more influenced by shingle color and orientation to the sun, the interior climate and the resulting consequences are what the real life experiences have shown to me.

Inadequate ventilation has not only shortened the life of asphalt shingles but has also compromised the structural components they are attached to.

I have photos of a home I inspected this week. The 25 year 3-tab shingles are precisely 10 years old. This is an accurate estimate by the home owner, because she put on the new roof when she purchased the home. They are completely deteriorated due to inadequate ventilation installed by another roofing contractor. Additionally, the newly installed OSB decking which was also installed at that time has severe sumps and deterioration occurring as well.

Also, I have photos from a job I did exactly 9 years ago this coming September, which had the proper amount, (more than required), of exhaust ventilation installed. These shingles from the same manufacturer as the degraded ones look as good today as the day they were installed, with the exception of pitted shingles under an antennae, where the bird droppings continually land and eat through the product.

I will post side by side photos for comparison later for review.

I am glad you came back to this thread, but I would be interested in your interpretation of the links and comments from my previously made two posts to see if you feel they have any merit.

Ed

Brian,

Since the article was not dated when I was doing my research, I had fugured that it was from some time ago. I know you have a firm stance regarding this topic and it did not seem to jive with your current views.

Did you happen to have time to review my previous back to back posts, excerpted comments, and the linkds they came from yet?

My trouble with your stance is that I have seen the structural devestation on deck sheathing from inadequate ventilation. Although the roof surface temperatures may likely be more influenced by shingle color and orientation to the sun, the interior climate and the resulting consequences are what the real life experiences have shown to me.

Inadequate ventilation has not only shortened the life of asphalt shingles but has also compromised the structural components they are attached to.

I have photos of a home I inspected this week. The 25 year 3-tab shingles are precisely 10 years old. This is an accurate estimate by the home owner, because she put on the new roof when she purchased the home. They are completely deteriorated due to inadequate ventilation installed by another roofing contractor. Additionally, the newly installed OSB decking which was also installed at that time has severe sumps and deterioration occurring as well.

Also, I have photos from a job I did exactly 9 years ago this coming September, which had the proper amount, (more than required), of exhaust ventilation installed. These shingles from the same manufacturer as the degraded ones look as good today as the day they were installed, with the exception of pitted shingles under an antennae, where the bird droppings continually land and eat through the product.

I will post side by side photos for comparison later for review.

I am glad you came back to this thread, but I would be interested in your interpretation of the links and comments from my previously made two posts to see if you feel they have any merit.

Ed

Brian,

Since the article was not dated when I was doing my research, I had fugured that it was from some time ago. I know you have a firm stance regarding this topic and it did not seem to jive with your current views.

Did you happen to have time to review my previous back to back posts, excerpted comments, and the linkds they came from yet?

My trouble with your stance is that I have seen the structural devestation on deck sheathing from inadequate ventilation. Although the roof surface temperatures may likely be more influenced by shingle color and orientation to the sun, the interior climate and the resulting consequences are what the real life experiences have shown to me.

Inadequate ventilation has not only shortened the life of asphalt shingles but has also compromised the structural components they are attached to.

I have photos of a home I inspected this week. The 25 year 3-tab shingles are precisely 10 years old. This is an accurate estimate by the home owner, because she put on the new roof when she purchased the home. They are completely deteriorated due to inadequate ventilation installed by another roofing contractor. Additionally, the newly installed OSB decking which was also installed at that time has severe sumps and deterioration occurring as well.

Also, I have photos from a job I did exactly 9 years ago this coming September, which had the proper amount, (more than required), of exhaust ventilation installed. These shingles from the same manufacturer as the degraded ones look as good today as the day they were installed, with the exception of pitted shingles under an antennae, where the bird droppings continually land and eat through the product.

I will post side by side photos for comparison later for review.

I am glad you came back to this thread, but I would be interested in your interpretation of the links and comments from my previously made two posts to see if you feel they have any merit.

Ed

Brian,

Since the article was not dated when I was doing my research, I had fugured that it was from some time ago. I know you have a firm stance regarding this topic and it did not seem to jive with your current views.

Did you happen to have time to review my previous back to back posts, excerpted comments, and the linkds they came from yet?

My trouble with your stance is that I have seen the structural devestation on deck sheathing from inadequate ventilation. Although the roof surface temperatures may likely be more influenced by shingle color and orientation to the sun, the interior climate and the resulting consequences are what the real life experiences have shown to me.

Inadequate ventilation has not only shortened the life of asphalt shingles but has also compromised the structural components they are attached to.

I have photos of a home I inspected this week. The 25 year 3-tab shingles are precisely 10 years old. This is an accurate estimate by the home owner, because she put on the new roof when she purchased the home. They are completely deteriorated due to inadequate ventilation installed by another roofing contractor. Additionally, the newly installed OSB decking which was also installed at that time has severe sumps and deterioration occurring as well.

Also, I have photos from a job I did exactly 9 years ago this coming September, which had the proper amount, (more than required), of exhaust ventilation installed. These shingles from the same manufacturer as the degraded ones look as good today as the day they were installed, with the exception of pitted shingles under an antennae, where the bird droppings continually land and eat through the product.

I will post side by side photos for comparison later for review.

I am glad you came back to this thread, but I would be interested in your interpretation of the links and comments from my previously made two posts to see if you feel they have any merit.

Ed

Brian,

Since the article was not dated when I was doing my research, I had figured that it was from some time ago. I know you have a firm stance regarding this topic and it did not seem to jive with your current views.

Did you happen to have time to review my previous back to back posts, excerpted comments, and the links they came from yet?

My trouble with your stance is that I have seen the structural devastation on deck sheathing and shingles via comparison from similar time frames and manufacturers completely resulting from inadequate ventilation. Although the roof surface temperatures may likely be more influenced by shingle color and orientation to the sun, the interior climate and the resulting consequences are what the real life experiences have shown to me.

Inadequate ventilation has not only shortened the life of asphalt shingles but has also compromised the structural components they are attached to.

I have photos of a home I inspected this week. The 25 year 3-tab shingles are precisely 10 years old. This is an accurate estimate by the home owner, because she put on the new roof when she purchased the home. They are completely deteriorated due to inadequate ventilation installed by another roofing contractor. I would havew guessed the shingle age to be between 25-30 years old. Additionally, the newly installed OSB decking which was also installed at that time has severe sumps and deterioration occurring as well.

Also, I have photos from a job I did exactly 9 years ago this coming September, which had the proper amount, (more than required), of exhaust ventilation installed. These shingles from the same manufacturer as the degraded ones look as good today as the day they were installed, with the exception of pitted shingles under an antennae, where the bird droppings continually land and eat through the product.

I will post side by side photos for comparison later for review. This way you can see a 9 year old roof wth proper ventilation and a 10 year old roof with inadequate ventilation from the same manufacturer, side by side for a true aging comparison.

I am glad you came back to this thread, but I would be interested in your interpretation of the links and comments from my previously made two posts to see if you feel they have any merit.

Ed

Ed :
Have been working on a answering those posts but get attracted to others at times. Starting to run out of time again as $$$$ work is backing up!

No problem. I would rather have an accurate well thought out responce rather than a fast responce just for the sake of responding.

Ed

Here’s a website from Certainteed: http://files.buildsite.com/dbderived-f/certainteed/derived_files/derived94782.pdf

Excerpt from article with all its flaws:

**In an ideal world, ventilation standards to establish proper air flow levels would take into account attic design characteristics and the performance of various ventilation products. But such codes and changes are not likely to emerge any time soon, so the following standards and measurements provide some guidance:
**

**• One way to measure ventilation is called **

net free vent area — a measurement of a vent’s unrestricted opening. According to most building codes, for every 150 square feet of attic floor, designers should provide 1 square foot of net free area of vent.
• You can reduce this ratio to one square foot of vent for every 300 square feet of attic space if you use an effective vapor retarder in the ceiling, or if there is approximately an even split of vent net free areas between the ridge (exhaust) and eaves (intake) areas.
**They reduce the venting by 50% when an unsealed vapour retarder is in place but…we all know that 98% of moisture movement is AIR LEAKAGE, not vapour diffusion. This just doesn’t jive- reduce venting requirements by 50% when the added measure, a vapour retarder, stops only another 2% of moisture. These people need to go back to school and learn the old math. By reducing the moisture flow upward by 2% with a vapour retarder, the vent ratio should be 1:153!!!

• Ideally, 50 percent of the required ventilating areas should be provided by vents inthe upper attic near the ridge, while the remaining 50 percent is located at eave/soffitvents. **It should be noted, however, that these 1/150 and 1/300 ratios are minimum standards and may not be enough to prevent ice dams, nor is net free area any indication of actual air flow.
I’ve posted info from others to this effect in the past 2 weeks. So if you don’t know if the actual amount of venting you are going to put in will have the desired airflow…what the heck. Venting is far from a science although it is pushed by many as being one. I mentioned something in a post about the actual flow through the small orifices of soffits and later saw something by some one who obviously had some physics experience also questioning the concept of net free area.

**• Another way to tally ventilation is air flow — commonly measured in
**

**CFM — the amount of cubic feet of air moved per minute. Systems with the same net free areas can vary widely in air flow, which affects their performance. And unfortunately, most building codes don’t address CFM. That means that you could meet codes and still not be providing the proper amount of air flow for adequate ventilation. Research shows that proper venting provides 1.5 CFM of air flow per square foot (1.5 CFM/ft2) to expel heat in summer and 0.5 CFM of air flow per square foot (0.5 CFM/ft2) in winter to expel moisture and help prevent ice dams.
**

Are they talking about attic area or roof area? The steeper the roof, the faster the shingle area to be cooled grows!! Can they supply us with the research?

**• A third way to measure ventilation is **ACH — air changes per hour — which takes into account that attics with different roof pitches have different air volumes even though they may have the same floor area. Therefore, roofs with different pitches can have the same CFM/ft2 value but have different ACH requirements.

**M E A S U R E S O F S U C C E S S
**

***Seems to me the expert folks at Certainteed are struggling to get a “scientific” way to prescribe the amount of ventilation needed. How can a roofer be expected to know what really works. Overventilate in a snowy climate and have snow blow in. Increase ventilation in any non-airsealed attic/roof and increase the heat loss and in a wet house situation, possibly cause more moisture problems in the attic. It’s the roofers choice!! If I were a roofer and read this stuff, I’d be more confused since they just picked apart the 1:150 and 1:300 rules. (well, with a little outside help also)


Brian,

Short answer for now.

That information you posted is from the “Principles Of Attic Ventilation”, by the Air Vent Corporation, who I know you despise because you feel they only want to sell more ventilation products.

Check out the last 3-4 pages of that free pubvlication available via their website as a pdf download.

The alternative methods of ventilation calculation are based on other studies from alternate organizations. Their intent was not to confuse a roofer, (I understood it), but to offer additional sources of information and to show that even more than the 1/150 or 1/300 should actually be called for.

I have installed thousands of feet of the ridge vent which contains the external baffle and have never had weather infiltration.

I also have installed the unbaffled Cobra Vent and the unbaffled Roll Vent and with both of those products I had a total of 4 instances over 2 year period of time which allowed 2 snow and 2 rain infiltrations into the attic. Since 1991, I have had ZERO problems with the Shingle Vent II by Air Vent.

I personally would expect a triangular gable vent to allow weather to enter. Even without scientific studies, a casual ,look at the installation of the product would lead me to believe it was not weather tight.

Som goes it for my short responce.

Ed

Here are the photos of 2 roofs, the good lookong one is 9 years old and the deteriorated looking one is 10 years old. (A different contractor did the decrepit one with less than minimal attic exhaust ventilation.)

They both have Tamko 25 year 3 thab shingles installed on them. The only significant difference between the 2 roofs is the attic exhaust ventilation.

I usually write much longer posts, but as they say, a picture is worth a thousand words.

Whoops! I forgot to resize the photos for posting. I’ll be back shortly.

Ed

Photos of 10 year old roof with inadequate ventilation.

Lauk 3.JPG

Lauk 1.JPG

Lauk 2.JPG

Lauk 4.JPG

Photos of 9 year old roof with adequate or better exhaust ventilation.

Nathani, Resized for internet posting, 100.jpg

Nathani, Resized for internet posting, 100.jpg

Nathani, Resized for internet posting, 100.jpg

Nathani, Resized for internet posting, 100_4717.JPG

Nathani, Resized for Internet Posting, 100_4710.JPG

Nathani, Resized for internet posting, 100_4707.JPG

The document I referred to is definitely through or from Certainteed as it was in the URL and mentioned a few times throughout the article. Maybe Certainteed owns Air Vent!!! Sneaky!! Isover Saint-Gobain is a huge multinational in the building industry.

No, I don’t despise the vent people but have a healthy disrepect because they never seem to mention anything about attic airsealing to save energy, reduce the need for winter venting, and help reduce the need for a winter humidification in cold climates, all building science items.

Actually not many people seem to want to learn building science since it makes them have to read, crunch the concepts (ouch!) and, in many cases, change their minds and forget some of the BS (building science) learned at the street level. Oh! And most of these courses aren’t free; they have to take time off/make time on nights or weekends and pay for their upgraded education. What a concept in an entrepreneurial capitalist system!!

Here’s a quote from one of the world’s foremost building scientists from the end of a talk to the Alberta Building Envelope Council AGM. (I believe):

“It was once suggested that one problem in transferring technology in the building industry is that nobody reads anything. It may be equally valid today since practitioners, as well as many researchers in building and construction seem to have neglected to read or re-read the CBD’s (Canadian Building Digests), even those that fall into their respective areas of interest.”

The rest of the paper is found here:
http://members.shaw.ca/alandalg/Gus_CBD.htm

Doing a search for this quote from Gus Handgord, a mentor to Joe Lstiburek, and found this from Energy Design Update (in case you haven’t seen one of their articles before):
http://www.1-800-arkansas.com/energy/files/Clearinghouse/Ordinary%20Paint%20as%20Replacement%20for%20Poly%20Vapor%20Retarder.pdf

Here’s a little on Gus from Building envelope forum:
http://www.buildingenvelopeforum.com/handegord.htm