Hey Guys,
Just wanting another educational moment with you all…
Have you ever been to an inspection and their was a Lightning Protection System…you know the ones with the rods on the roof and they lead down to their own ground rods…have you ever thought to yourself…are they bonding this thing correctly?
I found in a recent conversation with a few AHJ’s across the country they it is nearly 30% of them do not think the lightning system should be bonded with the grounding electrode system of the house…they say they need to be kept apart…well…the NEC see’s it differently.
If you have your CODE books handy…check out 250.106 and give it a look see…
**250.106 Lightning Protection Systems.
**The lightning
protection system ground terminals shall be bonded to the
building or structure grounding electrode system.
FPN No. 1: See 250.60 for use of air terminals. For further
information, see NFPA 780-2004,
Standard for the Installation
of Lightning Protection Systems, which contains detailed
information on grounding, bonding, and spacing from
lightning protection systems.
FPN No. 2: Metal raceways, enclosures, frames, and other
non–current-carrying metal parts of electric equipment installed
on a building equipped with a lightning protection
system may require bonding or spacing from the lightning
protection conductors in accordance with NFPA 780-2004,
*Standard for the Installation of Lightning Protection Systems
*
.
Separation from lightning protection conductors is
typically 1.8 m (6 ft) through air or 900 mm (3 ft) through
dense materials such as concrete, brick, or wood.
Also check out 250.60 as well…
**250.60 Use of Air Terminals.
**Air terminal conductors and
driven pipes, rods, or plate electrodes used for grounding air
terminals shall not be used in lieu of the grounding electrodes
required by 250.50 for grounding wiring systems and equipment.
This provision shall not prohibit the required bonding
together of grounding electrodes of different systems.
FPN No. 1: See 250.106 for spacing from air terminals.
See 800.100(D), 810.21(J), and 820.100(D) for bonding of
electrodes.
[size=2]FPN No. 2: Bonding together of all separate grounding
electrodes will limit potential differences between them and
between their associated wiring systems.
So…when looking at the electrical systems…and you notice a lightning protection system on the roof…see if the lightning system is installed correctly…you may be surprised.
Does this go above and beyond your scope…yep it might…but for educational puposes figured you might like to know…
This is for Educational Purposes Only…Paulright Protected ![/size]