Originally Posted By: pabernathy
This post was automatically imported from our archived forum.
David, Your questions were as followed:
Q.How do we handle this information?
I see neutral and ground wires under the same terminal screw all the time!
A. Answer: Only one grounded (neutral) conductor can be secured in a single neutral bar terminal in a panelboard. An exception allows two or more paralleled conductors in one termination if the terminal is listed for more than one conductor ( of the same size/AWG).( NEC 408.21 2002 version)
1. New construction: I can see calling attention to this and recommend change. The subcontractor is on site or down the street as it may be.
A- Answer :They should gladly change it and thank you for making them aware of it. You would surprised how many electricians who work all day and do not have time like me, joe, bob and greg do to keep up on it...lol
2. Existing construction: is this code enforcement by recommending the panel being reworked?
A- Well it has been a practice I have seen before as well and usually their is enough room to solve the problem before even thinking about having to add another termination bar.....But I would by all means mention it since you are in the panel.
The intent of this requirement is to ensure that the grounded ( neutral ) conductor of a multiwire branch circuit is not momentarily disconnected, which could result in a destruction of electrical equipment and fires from overvoltage. ( note...if it is a multiwire circuit and in some olders homes it was done...we do not do it nearly as much today...tooo Taboo ! )
If two grounded ( neutral ) conductors are connected to the same terminal, and someone removes one of the neutrals, the other neutral may be accidentially removed as well....if this is done it could cause a excessive line to neutral voltage for one of the circuits.....if in a multiwire circuit...This was the original intent of the ruling.
Now under Art 110.3(b) "2002 version " which requires the equipment to be installed as the manufacturer lists ( instructions and markings ). Their are even a few panels ( UL 67 standards ) that allow upto (3) 10 AWG Eq. grounds to terminate in a single terminal, if the terminal is marked for this purpose.
Hope this explains it a bit......probably more info than you wanted but you can always use this to explain to the contractor WHY...now they will say...but their is no multi-wire circuits on it.....and to that I say...how do you know...did you wire it?...if they say Yes I did....you say...well see now you have learned something new my friend......Kiss Me...
Ok...you might want to leave out the Kiss Me part....
--
Paul W. Abernathy- NACHI Certified
Electrical Service Specialists
Licensed Master Electrician
Electrical Contractor
President of NACHI Central Virginia Chapter
NEC Instructor
Moderator @ Doityourself.com