Is that a FL thing Dave? I can’t recall ever seeing lugs covered like that on new homes, around here anyway.
It has been in the NEC for several code cycles. This is from the 2020 NEC:
230.62(C) Barriers.
Barriers shall be placed in service equipment such that no uninsulated, ungrounded service busbar or service terminal is exposed to inadvertent contact by persons or maintenance equipment while servicing load terminations.
Just learned something. Thanks Robert. I suppose our local AHJs don’t look for that. Time to update my report software.
No my understanding it is NEC requirement.
Thanks Robert.
Image updated: Main Disconnect - Inspection Gallery - InterNACHI®
We updated: Main Disconnect - Inspection Gallery - InterNACHI®
Hit refresh.
I don’t think the barrier is required for the grounded conductor.
Correct. Not required.