No electrical conduit to AC condenser... safety hazard?

Originally Posted By: jrabanus
This post was automatically imported from our archived forum.



I found that there was no electrical conduit for the AC condenser. Should I write this up as a safety hazard?


Josh Rabanus

[ Image: http://www.nachi.org/bbsystem/usrimages/more/DSCN2219.JPG


Originally Posted By: jpope
This post was automatically imported from our archived forum.



That appears to be your standard NM (Romex). It is listed for dry locations only and is required to be protected from damage.


So yes, this application, to me, appears to be a potential safety hazard.


--
Jeff Pope
JPI Home Inspection Service
"At JPI, we'll help you look better"
(661) 212-0738

Originally Posted By: jschwartz1
This post was automatically imported from our archived forum.



Josh,


I also believe that electrical tape is typically not used in outdoor weather conditions. ![eusa_naughty.gif](upload://nYl3dmRmAIH81yCdH9V96akYnNa.gif)

Jay


Originally Posted By: fwalker
This post was automatically imported from our archived forum.



Flexable conduit of course. Rigid can’t take the vibration.


Originally Posted By: jpeck
This post was automatically imported from our archived forum.



fwalker wrote:
Flexable conduit of course.


Say what?

Can you be more specific (please)?

Remember, that is OUTDOORS.


--
Jerry Peck
South Florida

Originally Posted By: fwalker
This post was automatically imported from our archived forum.



I am aware of the fact that the condenser unit is out side of the house. Since it houses the compressor it vibrates. Water tight “flexable” conduit should be used. hard tube conduit is subject to crack. icon_cool.gif


Originally Posted By: Darcy Heron
This post was automatically imported from our archived forum.



This might help!!


http://www.nachi.org/bbsystem/usrimages/more/Air.jpg[/img]
http://www.nachi.org/bbsystem/usrimages/more/Flexible.jpg[/img]


Originally Posted By: fwalker
This post was automatically imported from our archived forum.



Jery, Please refer to Darcy’s picture. It will show you what I am talking about.


Originally Posted By: jpeck
This post was automatically imported from our archived forum.



fwalker wrote:
Water tight "flexable" conduit should be used.


That's why I wanted you to be more specific.

'Flexible conduit' is not liquidtight conduit, and it needed to be liquidtight conduit too.

Either liquidtight flexible metal conduit or liquidtight flexible non-metallic conduit


--
Jerry Peck
South Florida

Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



I agree that these A/C units are usually wired with SealTite but I am not sure why you can’t use UF, SE or wet location MC. It is supported within 12" of the connector. Anyone got a code reference?


I would question the Romex connector tho. If a “cable” is legal it would still need a wet location connector.


The mechanical code will probably have a problem with supporting the cable on the Freon line and that may really be the violation.


Originally Posted By: jrabanus
This post was automatically imported from our archived forum.



This helps me alot thanks guys. Darcy, thanks for the pics.


Josh Rabanus


Originally Posted By: bbadger
This post was automatically imported from our archived forum.



Good luck finding a code reference that rigid conduit can not be used. icon_lol.gif



Bob Badger


Electrical Construction & Maintenance


Moderator at ECN

Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.



Bob I imagine the real reason HVAC techs use sealtite is because it is easy. Bending conduit may be a trick they are not willing to learn.


Usually the EC stops at the disconnect.


These new condensers don’t really vibrate that much (at least not the outer case) and I agree there is no code reason why you can’t use pipe.


Originally Posted By: bbadger
This post was automatically imported from our archived forum.



Hi Greg, here we wire all the way to the unit and I have never used rigid all the way.


I just wanted to point out the lack of code rules in regards to vibrating equipment.

Strangely enough typical MC would be NEC compliant. ![icon_confused.gif](upload://qv5zppiN69qCk2Y6JzaFYhrff8S.gif)

Bob


--
Bob Badger
Electrical Construction & Maintenance
Moderator at ECN