I have never seen this before, where is the electrical mast ?? I know this is a 1900 built house, but what happened

The attachment directly to the home used to be common, but:
- There’s no drip loop;
- Service entrance conductors have to be protected from abrasion.
- Service entrance conductors need to be enclosed within a proper raceway.
Improper installation should be corrected by a qualified electrical contractor.
The siding crew buried the SEC behind the vinyl siding. Just wait until someone nails something into the conductors 
Perfect, Thanks
Yeah that is not right! ZZaap! ![]()
WOW just wow.