No electrical mast

I have never seen this before, where is the electrical mast ?? I know this is a 1900 built house, but what happened DSCN1562 DSCN1563 DSCN1565

The attachment directly to the home used to be common, but:

  1. There’s no drip loop;
  2. Service entrance conductors have to be protected from abrasion.
  3. Service entrance conductors need to be enclosed within a proper raceway.

Improper installation should be corrected by a qualified electrical contractor.

The siding crew buried the SEC behind the vinyl siding. Just wait until someone nails something into the conductors :smiley:

Perfect, Thanks

Yeah that is not right! ZZaap! :roll_eyes:

WOW just wow. :joy: :joy: