Obstructed panel

With wires on the outside of the panel going in the panel?

The wires are coax cable and telephone lines which look like they are above and below the panel, and not going into the panel itself. At least that what it looks like to me.

Wrong AC breaker protection. 30 instead of 25

Double lugged neutrals

12 AWG protected by 30A

Curious, what was the #12 on the 30 amp OCPD feeding the AC?

No, it was feeding 3 12 AWG circuits.:frowning:

10 AWG on the 30A AC breaker but max is supposed to be 25A

No OCP at the exterior disconnect.