I recently inspected a home that the fill and vent pipe were in a attached garage. I advised the client I did not believe this was ok and that they should be on the exterior of the home. I called the oil supplier for the home and inquired (just said one of their customers i did not tell them address). They said it is not code and if they thought it was unsafe they would require it be addressed. So I said ok. I called another provider and inquired just to be diligent since I was obviously ignorant. They gave they same answer. Now I was under the impression these had to go to the exterior?
Soooo I am curious what all have to say or point out (even if obvious). I did point it out if anyone is curious I figured I would protect my butt and let them decide.
Reason I am even mentioning is I just did a home that the fill was in a basement which is only accessible thru a 25ft+ deep attached garage. If I call this provider for the client and they say the same I feel that makes me look dopey to all involved since they are the pro. Again I did put it in the report. anyway.
M2203.3 Fill piping. Fill piping shall terminate outside of buildings at a point at least 2 feet (610 mm) from any building opening at the same or lower level. Fill openings shall be equipped with a tight metal cover.
M2203.5 Vent termination. Vent piping shall terminate outside of buildings at a point not less than 2 feet (610 mm), measured vertically or horizontally, from any building opening. Outer ends of vent piping shall terminate in a weather-proof cap or fitting having an unobstructed area at least equal to the cross-sectional area of the vent pipe, and shall be located sufficiently above the ground to avoid being obstructed by snow and ice.
I am sorry if I wrote it poorly. They stated that having it in the garage was not against code. If they thought there were a issue they would of required it to be fixed.