pmagrone
(PAUL MAGRONE, Florida License # HI 30)
1
If the main disconnect is located in the garage and that is the only panel present, do the ground wires and neutral wires have to be separate? This panel looks very sloppy to me the way the ground and neutral wires are run to the buss. Some are sharing the same lug. How would you write this in the report?
That is what you call very sloppy? At the rist of sounding narcissistic mine are a bit neater but that looks fine to me.
I have to say, here in NY that method of terminating grounds and neutrals of the same circuit is generally accepted by inspectors and MANY quality electricians do it that way. I did for many years, but do not any more.
We do NOT follow the NEC and I have had high level inspectors tell me it’s fine.
Take that for what it’s worth.
pmagrone
(PAUL MAGRONE, Florida License # HI 30)
10
Thanks for the help. So, this is alright? As long as there are not two neutral wires to one lug?
For the record: I understand the issue most folks have with this, but those photos are NOT the same thing. Doubling neutrals is not the same issue as in the original post.
Yea now I see it. Guess I am so blind I need to be lead to the point before I know that I am there :mrgreen: :mrgreen:
pmagrone
(PAUL MAGRONE, Florida License # HI 30)
16
Thanks. One more question…do you call it? I did call it but did once before only to have a licensed electrician say it was fine. What do you suggest?:mrgreen: </IMG>
The grounded and grounding conductors must be isolated from one another unless there are no continous metallic paths (conduit, equipment grounding conductor) between the main panel and the sub panel. If there is no continous metallic path, they must be connected together.
It is not allowable to put more than one conductor under a screw unless they terminals are specifically identified as being suitable for the purpose. It does not matter what the use of the conductors is. The same rule applies for grounded, grounding, and ungrounded conductors.
The connections in Mike Holt’s graphic are OK, not because they are grounded and grounding conductors but, because the terminals are rated for more than one conductor.
Conductors should not extend more than 1/4" beyond the terminal.
Grounds cannot be ganged together. This requirement has been under NEC Article 110.14(a) for as long as I can remember. I started as an apprentice electrician working under the 1971 NEC and that’s the way we were taught even then. It may have been in a different place in the NEC back then. I am almost certain that it has been in 110.14(a) at lease since the 1993 NEC.