Home built in 2001, panel and meter appear to be original. So I just wanted to make sure I am correct on this. Hard to believe it was originally wired this way, but who knows, right?
Service Panel has a 200 amp breaker, but the feeders are only TWHN-2, which according to my handy chart is only good for 100 amps. Just wanted to make sure I wasnt missing something here.
Looks like the main breaker could be newer, but still, this is a 2000 sf home, shouldnt have been wired with only 100 amps 20 years ago.
Don’t let your mind play trix with you There is a name for this… when you read or hear something and your mind makes a different association with the object.
That table is for standard conductor ampacities. For a dwelling service the service conductors are required to only be 83% of the OCPD size so 200 amps * 83%=166 amps minimum conductor size for 200 amps. From that table #2/0 Cu at 75° C= 175 amps so you’re good.
I assume that it is carrying 100%. I just wanted to point out the 100% because many people undersize feeders (like to sub panels) using the 83% rule for ‘other’ conductors.
Why would you assume? The photo’s clear show that the meter is feeding only the service. If you wanted to reference sub-panels you could have just said that.
the 83% only applies if the entire load is on the conductors (single set). If you have 2 200 AMP panels the 4/0 AL would be limited to 180 AMPS since the entire load is split and not to one panel. 2017 NEC pp-70-149
EDIT:
Getting old. I have passed this very example. My point was supposed to be that the 83% rule only applies to carrying the entire load.
Yeah, I was Just implying I have never seen a 100 amp service on any single family home built in the past 60 years or so.
I know it could still be acceptable
amazing…I worked a lot of new construction in the 70’s (never as an electrician) but the standard panel was usually 100 amp for Your basic 1500 to 2000 sq ft home…we must have been way behind…