Hey Guys-

Is it okay to pigtail two conductors in a panel to avoid double-tapping a breaker? Or at least that is what it seems they were doing here since both conductors could have made it to the breaker on their own. Thanks.

Kenny

i27.jpg

i27.jpg

i29.jpg

Better than a double tap and they accept here.

Those are allowed. Look at 312.8 NEC.

They might not even be needed, some CH can have two conductors.

Common practice

Generally, that is an acceptable correction to a double-tapped breaker.

I see double-taps all the time but this was the first time I’ve seen someone take the extra step to avoid doing it. Thanks, I appreciate the replies.

Kenny

Perfectly acceptable. Did you see the upen knock-out at the top of the panel?