Under what conditions is wiring allowed to be in or through ducts or plenums used for HVAC?
–
Jerry Peck
South Florida
Originally Posted By: jpeck
This post was automatically imported from our archived forum.
–
Jerry Peck
South Florida
Originally Posted By: jtedesco
This post was automatically imported from our archived forum.
Quote: |
Plenum. A compartment or chamber to which one or more air ducts are connected and that forms part of the air distribution system.
300.22(B) Ducts or Plenums Used for Environmental Air. Only wiring methods consisting of Type MI cable, Type MC cable employing a smooth or corrugated impervious metal sheath without an overall nonmetallic covering, electrical metallic tubing, flexible metallic tubing, intermediate metal conduit, or rigid metal conduit without an overall nonmetallic covering shall be installed in ducts or plenums specifically fabricated to transport environmental air. Flexible metal conduit and liquidtight flexible metal conduit shall be permitted, in lengths not to exceed 1.2 m (4 ft), to connect physically adjustable equipment and devices permitted to be in these ducts and plenum chambers. The connectors used with flexible metal conduit shall effectively close any openings in the connection. Equipment and devices shall be permitted within such ducts or plenum chambers only if necessary for their direct action upon, or sensing of, the contained air. Where equipment or devices are installed and illumination is necessary to facilitate maintenance and repair, enclosed gasketed-type luminaires (fixtures) shall be permitted. |
--
Joe Tedesco, NEC Consultant
www.nachi.org/tedescobook.htm
Originally Posted By: jpeck
This post was automatically imported from our archived forum.
--
Jerry Peck
South Florida
Originally Posted By: jtedesco
This post was automatically imported from our archived forum.
--
Joe Tedesco, NEC Consultant
www.nachi.org/tedescobook.htm
Originally Posted By: jpeck
This post was automatically imported from our archived forum.
jtedesco wrote: |
Jerry:
What part of this rule you are having trouble understanding? How would others see or read this rule in any other way? The rule is clear and does not allow methods that are not included in the text. ![icon_biggrin.gif](upload://iKNGSw3qcRIEmXySa8gItY6Gczg.gif) |
--
Jerry Peck
South Florida
Originally Posted By: jtedesco
This post was automatically imported from our archived forum.
--
Joe Tedesco, NEC Consultant
www.nachi.org/tedescobook.htm
Originally Posted By: jpeck
This post was automatically imported from our archived forum.
jtedesco wrote: |
What exception are you talknig about? |
--
Jerry Peck
South Florida
Originally Posted By: jtedesco
This post was automatically imported from our archived forum.
Quote: |
Flexible metal conduit and liquidtight flexible metal conduit shall be permitted, in lengths not to exceed 1.2 m (4 ft), to connect physically adjustable equipment and devices permitted to be in these ducts and plenum chambers. |
--
Joe Tedesco, NEC Consultant
www.nachi.org/tedescobook.htm
Originally Posted By: jpeck
This post was automatically imported from our archived forum.
--
Jerry Peck
South Florida
Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.
Originally Posted By: jpeck
This post was automatically imported from our archived forum.
Greg Fretwell wrote: |
Are you asking if a homeowner can fish an MC cable from the 2d floor to the panel in the basement via the ductwork? |
--
Jerry Peck
South Florida
Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.
Originally Posted By: jpeck
This post was automatically imported from our archived forum.
Greg Fretwell wrote: |
Jerry do you think MC cable is a device or equipment? |
Quote: |
I see the cheese out there but I am not sure where the trap is that you want us to stick our head in. |
--
Jerry Peck
South Florida
Originally Posted By: roconnor
This post was automatically imported from our archived forum.
--
Robert O'Connor, PE
Eagle Engineering ?
Eagle Eye Inspections ?
NACHI Education Committee
I am absolutely amazed sometimes by how much thought goes into doing things wrong
Originally Posted By: jpeck
This post was automatically imported from our archived forum.
roconnor wrote: |
I dont agree that wiring is "equipment", |
--
Jerry Peck
South Florida
Originally Posted By: roconnor
This post was automatically imported from our archived forum.
--
Robert O'Connor, PE
Eagle Engineering ?
Eagle Eye Inspections ?
NACHI Education Committee
I am absolutely amazed sometimes by how much thought goes into doing things wrong
Originally Posted By: jpeck
This post was automatically imported from our archived forum.
roconnor wrote: |
Did you come across a situation in a home inspection where this became an issue? |
--
Jerry Peck
South Florida
Originally Posted By: Greg Fretwell
This post was automatically imported from our archived forum.
Originally Posted By: roconnor
This post was automatically imported from our archived forum.
Greg Fretwell wrote: |
... isn't the only real change to 300.22(B) the deletion of liquidtite FMC as an approved method? |
--
Robert O'Connor, PE
Eagle Engineering ?
Eagle Eye Inspections ?
NACHI Education Committee
I am absolutely amazed sometimes by how much thought goes into doing things wrong
Originally Posted By: bbadger
This post was automatically imported from our archived forum.
Quote: |
Service. The conductors and equipment for delivering electric energy from the serving utility to the wiring system of the premises served. |
Quote: |
This is not a trap. This is simply something I found out and am sharing. |
--
Bob Badger
Electrical Construction & Maintenance