Hi to all,
Here is todays question.
Regards
Gerry
Picture courtesy Charles Buell
Hi to all,
Here is todays question.
Regards
Gerry
Picture courtesy Charles Buell
Gerry,
Thats one of those inline traps right.
Lousy supports and not enough of them . Roy Cooke
Hi to all
the correct answer to this is:
**1 in 96
**Regards
Gerry
Ontario Building Code 1997
says 7.4.8.1 Minimum Slope and length of Drainage pipes
(1) Every drainage pipe that has a size of 3in. or less, and every fixture drain shall have a downward slopein the direction of flow of at least 1 in 50
Strange that there can be that much difference in our codes .
Roy Cooke
Gerry,
This is from the IRC:
“Drainage fittings shall be designed to maintain one-fourth unit vertical in 12 units horizontal (2-percent slope) grade.”
*
“Horizontal drainage piping shall be installed in uniform alignment at uniform slopes not less than one-fourth unit vertical in 12 units horizontal (2-percent slope) for 2 1/2-inch (64 mm) diameter and less, and not less than one-eighth unit vertical in 12 units horizontal (1-percent slope) for diameters of 3 inches (76 mm) or more.”*
1/4" per foot for all drains min.
1/8" per foot for all Vents min.
I even own a level for plumbing, it has a second set of markings for 1/4" per foot slope.
It is very important to read the complete question. I failed to do that and choose 1/4 inch. This is the kind of question you have to look out for when taking a certification test.
Same here.
Hi to all,
that was a little mean of me, but proves the point that Greg stated.
This was one of those questions that is designed to be wrongly answered, and no it isn’t a trick question, it is corrected worded.
BTW, the full explaination is to be found in IRC 3005.3 or UPC 708.0
Regards
Gerry