Service mast is the drip loop required

What your thoughts about this service mast , is the drip loop required in this case.

I t looks to me that the function of the drip loop is accomplished. Looks good from here!

2 Likes

Probably no real issue with the “drip loop,” but I would be calling out the lack of roof clearance. General standard is 18" power line clearance from roof in this installation. Also would be calling out the lack of proper flashing around the mast.

4 Likes

That is a setup that I never see. The drop is anchored by a bracket on the roof, so there is no stress on the mast. Still, I’m with Ryan that a boot is needed on the mast.

5 Likes

Three words… “Wind Blown Rain”!!

2 Likes