Shared neutral pigtails on Arc Fault Breakers

Recently I’ve started seeing this in new construction. Two neutral pigtails from two separate arc fault breakers are twisted and installed on one neutral lug. Is this permissible for Square D arc fault breaker?

NO!
Panel Manufacturer and NEC both state that only ONE Neutral Conductor may fall under a bus bar lug!

3 Likes

Here the relevant NEC section:

408.41 Grounded Conductor Terminations.
Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor.
Exception: Grounded conductors of circuits with parallel conductors shall be permitted to terminate in a single terminal if the terminal is identified for connection of more than one conductor.

2 Likes