jfrederick
(Joshua Frederick)
April 1, 2010, 2:04pm
1
Never have seen this type before. Aluminum wiring for the dryer was single strand, but a heavier gauge (6 or 8 perhaps??). Breaker above uses stranded aluminum, which is what I normally see when aluminum wiring is used. House built in '89. Comments? I don’t think there’s any concerns, however, would appreciate any feedback/insight.
I realize pics aren’t the greatest.
sfogarty
(Sean Fogarty)
April 1, 2010, 4:48pm
2
The single strand would have the same issues as smaller gauge aluminum. I would report it.
jfrederick
(Joshua Frederick)
April 1, 2010, 5:53pm
3
Thanks, Sean. Anybody else have any feedback/insight??
gbeaumont
(Gerry Beaumont)
April 1, 2010, 6:19pm
4
Personaly I wouldn’t be reporting it, firstly the problem with single strand back between 1965-75 really only affected the 12-14 awg branch circuits, secondly the formulation of the alloys was changed in the mid 70’s to relieve the problem, a home build in 1989 could not contain suspect aluminum wiring.
Regards
Gerry
jfrederick
(Joshua Frederick)
April 1, 2010, 6:26pm
5
Thanks Gerry, that’s kind of what I was thinking. Have you (or anyone else) ever seen this type before??
jfrederick
(Joshua Frederick)
April 1, 2010, 6:29pm
7
Thank you. Have a great Easter holiday!
jallingham
(John Allingham)
April 3, 2010, 11:32pm
8
gbeaumont:
Personaly I wouldn’t be reporting it, firstly the problem with single strand back between 1965-75 really only affected the 12-14 awg branch circuits, secondly the formulation of the alloys was changed in the mid 70’s to relieve the problem, a home build in 1989 could not contain suspect aluminum wiring.
Regards
Gerry
Gerry
Do you have a link on that. I didn’t know aluminum was an alloy.
gbeaumont
(Gerry Beaumont)
April 4, 2010, 12:29am
9
Here you go John
http://www.southwire.com/commercial/ALBuildingWire30YrsOfReliability.htm
The stuff from the 60’-70’s was 1350 alloy which was replaced with 8000 series alloy
Gerry
jallingham
(John Allingham)
April 4, 2010, 3:07pm
10
Thanks Gerry, I never knew that.
bkelly2
(Brian Kelly, AZ Cert. # 60234)
April 8, 2010, 8:01pm
12
jfrederick:
Never have seen this type before. Aluminum wiring for the dryer was single strand, but a heavier gauge (6 or 8 perhaps??). Breaker above uses stranded aluminum, which is what I normally see when aluminum wiring is used. House built in '89. Comments? I don’t think there’s any concerns, however, would appreciate any feedback/insight.
I realize pics aren’t the greatest.
ZRequ
My State SOP requires me to report any Single Strand AL Wires…
Oddly enough so does the INACHI SOP…
Better call it out…
gbeaumont
(Gerry Beaumont)
April 9, 2010, 12:07am
13
A little knowledge is a dangerous thing
Regards
Gerry
bkelly2
(Brian Kelly, AZ Cert. # 60234)
April 9, 2010, 3:05am
14
If you want to tell people to disregard the INACHI SOP that is fine with me Gerry…
I just assumed reading your reply you were not familiar with what the INACHI SOP actually said…
I follow my State SOP and we are required to call out Single Strand Al wiring, period…
Because I seem to have a little more knowledge of the INACHI SOP than you is no reason to be sad my friend…
bsmith
(Bill Smith)
April 9, 2010, 12:25pm
15
Excellent info Gerry (as always) Thanks -