I inspected a house yesterday for an investor (pre-listing) and came across a 1st floor bedroom (closet included) with only (2) 3’ x 3’ windows.
I called it as an egress safety hazard (really its a blatent code violation) since the window opening is only 3.46 sq. ft. (32" wide x 15" tall clear opening)
I was building homes in 99’ and we were required to have 5.0 sf of open area on the 1st floor. He doesn’t agree with my reporting. (ha!)
Please chime in and let me know how you would have handled this one.
The investor thinks it shouldn’t be in the report because the building inspector passed it when the house was built… even know its wrong. Like a building inspector never misses anything. Really?
My reason for my answer even if it was a double hung window it would still reduce the exit opening unless the panels were totally removed
BTW It was not a stupid question but a interesting one. what does everyone think would it make a difference or not
mauger
(Mike Auger, CMI - RI 43685, RMC-142, RMB-096)
12
Nate, you don’t have time to remove windows in a fire, a rescue person may not be able to do it and in a child’s room, or elderly persons room, or non-mechanically inclined occupant, they cant do it. The home should be good for any situation. You need to get the minimum required opening by normal window operation.