**210.12 Arc-Fault Circuit-Interrupter Protection.
(A) De.nition: Arc-Fault Circuit Interrupter.
**An arc-fault circuit interrupter is a device intended to provide protection
from the effects of arc faults by recognizing characteristics unique to arcing and by functioning to de-energize the circuit when an arc fault is detected.
**(B) Dwelling Unit Bedrooms. **
All 120-volt, single phase,
15- and 20-ampere branch circuits supplying outlets installed
in dwelling unit bedrooms shall be protected by a
listed arc-fault circuit interrupter, combination type installed
to provide protection of the branch circuit.
Branch/feeder AFCIs shall be permitted to be used to
meet the requirements of 210.12(B) until January 1, 2008.
FPN: For information on types of arc-fault circuit interrupters,
**see UL 1699-1999, **
Standard for Arc-Fault Circuit
Interrupters**.**
*Exception: The location of the arc-fault circuit interrupter
*
shall be permitted to be at other than the origination of the
branch circuit in compliance with (a) and (b):
(a) The arc-fault circuit interrupter installed within
1.8 m (6 ft) of the branch circuit overcurrent device as
measured along the branch circuit conductors.
(b) The circuit conductors between the branch circuit
overcurrent device and the arc-fault circuit interrupter
shall be installed in a metal raceway or a cable with a
metallic sheath.
Ok…I am not aware of anything pending with the 2005 regarding this…
http://www.mikeholt.com/onlinetraining/page_images/1099599192_2.jpg
Revised text to require, after January 1, 2008 that all dwelling unit bedroom branch-circuit AFCI protection devices must be listed as a “Combination Type AFCI.” And new exception permits AFCI protection by a device that isn’t a circuit breaker (such as a receptacle), but only if it meets stringent requirements.
(B) Dwelling Unit Bedroom Circuits. All 15 or 20A, 120V branch circuits that supply outlets in dwelling unit bedrooms must be AFCI protected by a listed arc-fault circuit interrupter. Figure 210-10
Author’s Comment: Smoke detectors connected to a 15 or 20A circuit must be AFCI protected if the smoke detector is located in the bedroom of a dwelling unit. The exemption of AFCI protection for the fire alarm circuit [760.21 and 760.41] doesn’t apply to the smoke detector’s circuit, because a smoke detector circuit isn’t
defined as a fire alarm circuit; it’s an “alarm circuit” [See NFPA 72, National Fire Alarm Code].
After January 1, 2008 (basically a 2008 NEC requirement), AFCI protection shall be provided by a combination type AFCI protection device.
Author’s Comment: Combination Type AFCI protection devices provide improved safety performance over existing AFCI protection devices, because the combination type is designed to detect arcs as low as 5A peak. Existing branch-circuit AFCI circuit breakers are designed to operate when the arcs exceeds 75A peak. See UL 1699, Standard for Arc-Fault Circuit Interrupters (www.UL.com) for information on differences between a branch-circuit type AFCI and a combination type AFCI.
Ex: The location of the AFCI can be at other than the origination of the branch circuit if in compliance with (a) and (b). (a) The AFCI is installed within 6 ft of the branch-circuit overcurrent device as measured along the branch- circuit conductors. (b) The circuit conductors between the branch-circuit overcurrent device and the AFCI must be installed in a metal raceway or a cable with a metallic sheath.
Author’s Comment: The 120V circuit limitation means that AFCI protectionisn’t required for equipment rated 230V, such as baseboard heater or room air conditioner.
Hope this helps…Courtesy of Mike Holt. Figured this would explain it better .