I just inspected this home that has a main panel in the basement that is 100 Amp. The sub-panel in the garage is fed by a 60 amp breaker from the main panel. However the sub-panel has a 100 amp main breaker. So I should list this panel as 60 amps?
Also the sub panel has bare ground wires and white neutral wires connected at both sides. :roll:
Yes, if it’s fed at 60 amps, it’s only a 60 amp subpanel. The 100 amp breaker in that subpanel is nothing more than a “local disconnect”, making a convenient place to kill the power to the whole panel. It probably came with the subpanel when the original installer purchased it, actually.
Since as you have said before Mark , the sub panel does not need a main breaker , we can see it as a on off switch, but isn,t that misleading if somebody overloads the sub panelbased on it stated 100 amps.