Saw one of these units installed today. I noted both the unit was not secured to the cabinet and it was double tapped to an existing breaker. Turns out, UL has also published this unit is a potential fire hazard. Would you/have you informed the sellers about this component? Why/why not?

Details on the install below:

Note, this unit was included in an update to the article in 2019.

2 Likes

Unit must be secured and connected with the shortest lead wires possible and not be double-tapped. If UL says it is a fire hazard, I would definitely call it out and recommend removal.

2 Likes

Would you notify the sellers too?

If you now have that knowledge after report issue, I would email them & let them know your discovery.

2 Likes

Yes, I would notify the sellers.

2 Likes

Yes, I would notify the sellers.

Of what? Do you notify the sellers of all defects found?

2 Likes

No Dominic, just safety hazards as is stated in the SOP

3 Likes

Same here!

1 Like

Thanks everyone! I appreciate the perspective from each of you!