This water heater vent pipe termination looks to close to window openings, right???
Located in San Fernando Valley. Los Angeles, CA

20141016-75.jpg

The roof pitch if less than 6/12 and it appears so must be at least 1’3" above the roof and it appears so, and because of the vent does not extend above the adjacent roof, must be at least 8 feet from the wall… And is not. The solution is to extend above the adjacent roofline at least 2 feet. It’s not just a window issue it’s the entire wall.

Thanks. Thought so myself. The are other issues going on at the start of this vent pipe as well.

Here are a couple of tables / graphics that may come in handy if you do not already have… was on mobile earlier and did not have to post with my earlier comment.