This water heater vent pipe termination looks to close to window openings, right???
Located in San Fernando Valley. Los Angeles, CA
The roof pitch if less than 6/12 and it appears so must be at least 1’3" above the roof and it appears so, and because of the vent does not extend above the adjacent roof, must be at least 8 feet from the wall… And is not. The solution is to extend above the adjacent roofline at least 2 feet. It’s not just a window issue it’s the entire wall.
Thanks. Thought so myself. The are other issues going on at the start of this vent pipe as well.