WH exhaust flue touches shingles. Is it Ok?

The water heater was in the basement. The exhaust flue was very long. It touches the shingles as it passes the roofline. Technically I think it is wrong, but it’s such a long distance, is it really a big deal? How hot can it be by the time it goes up 35 ft to the roofline?

Would you call it out as a fire hazard? Would you call it out for a different reason?




2 Likes

This would be my thought exactly… never going to be a problem but is wrong. Are shingles a “combustible?”

Good to see you’re still “pussing out” and staying off 9:12 roofs 40+ feet up :slight_smile: :slight_smile: :slight_smile:

3 Likes

Commercial rated WH?
IMO, no way a natural draft WH with that long of a flue exposed to the elements will maintain the heat necessary for a positive draft.
Any indication of backdrafting?

4 Likes

:rofl: You know I can’t keep my feet on the ground.


10 Likes

Good point. It was pretty cold.
i put my hand at the top of the water heater to feel for airflow. and I looked for any staining, scorching. Its a regular 75 gallon NG water heater.

Interesting side note: the furnace had a similar BTU/Hr rating as the water heater but the exhaust for the furnace was 5 ft to the left (PVC pipes over the air conditioner). The tall exhaust for the WH seems excessive to me.




3 Likes
2 Likes

It is messing with the edge flashing?

1 Like

Yes I would mention it. Flue touching roof.

2 Likes

If anything, direct contact mechanical damage over time

1 Like

asdf

See, the funny thing is the squareish caulk lines on top/sides of where the B-vent comes through the wall. It looks like there was a square vent from a direct vent water heater previously. I’m guessing something funky happened and some guy replaced the direct vent water heater with a normal draft hood water heater that vented to the side wall. Next home inspector comes up and say you can’t vent like that… Homeowner didn’t want to spend the money to put in a brand new direct vent water heater since the water heater was just replaced so they paid someone to have it extended past the roof. Otherwise, I can’t see why anyone would go through all that work to run the B-vent up the side of the house to the roof since it looks like ass and takes more labor to do???

2 Likes

Location matters. It is Tennessee don’t cha’ know!

Yes, I would write it up as improper installation being in contact with the roof surface materials.

This makes for a good argument to install a gas WH with a power vent. :wink:

2 Likes

I didn’t see the TPR valve in that picture. Also wasn’t strapped in. Probably should have be elevated 18".

1 Like

May I also say, the metal chimney flue chimney is not vertical/plumb. Metal Chimney pipes require vertical wall bracing at a minimum of every 6-8 feet (depending on the manufacturer) up the side of the structure.

Hi Ray,
Thanks for taking a look and helping out with some possible defects. That picture was taken in the dark back corner of the basement so it may be hard to see the TPRV is on the left side of the tank in that picture. We don’t strap the tanks in Tennessee because we don’t often have earth quakes big enough to notice.
Here in my area a gas water heater only needs to be elevated 18" if it is in a garage and if it is not listed as flammable vapor ignition-resistant. CPSC mandated that all Gas water heaters be FVIR since 2002. This water heater was manufactured in 2016 and is in the basement.


I’ll add some cut-and paste info from website “How to look at a house”
All gas water heaters manufactured since late 2002, when the Consumer Products Safety Commission (CPSC) mandated that all water heaters be Flammable Vapor Ignition Resistant (FVIR), qualify for the exemption. It will be marked on the data plate on the side of the water heater that it is FVIR compliant.
When was a gas water heater first required to be elevated 18 inches above a garage floor? (howtolookatahouse.com)

5 Likes

When I zoom in, almost looks like a reducer bushing and a smaller pipe on the valve. Could just be an illusion though. :man_shrugging:

1 Like

Hot gases will never reach that roof line. Or escape that pipe.

1 Like

Now I see it…LOL…the red arrow helps…around here they’re all strapped and elevated no matter what. It makes me nervous seeing them sitting on the floor…especially since there’s a label with a guy catching fire on the water heater… but rules are rules I guess…thanks for the reply btw…

1 Like

I would have called it out just for the fact it’s wrong, dangerous? most likely not, I would also put in the report for approved permits to be obtained and then your client and you are covered.

1 Like

Some of the problems Ron is many local and state jurisdictions don’t require permits for a lot of renovations or retrofits. My area has none, zilch. HI’s in areas that require permits for replacement of systems assume all areas and jurisdictions do the same. So, it’s always best to check before general statements are put in a report.

2 Likes