How not to connect the GEC to the grounding busbar.
2 Likes
Bigger is better, Right?
at least its green.
Pure genius, how did the rest of the panel look?
1 Like
Everything else looked great, except for the pointed screws at cover. The way the rest of the wiring is I was really surprised when I saw the bonding screw.
2 Likes
Is this a service or a sub-panel? The installer made an effort to keep all of the EGC’s on the bus on the left and all of the neutrals on the bus on the right. The left and right side buses are still connected together. There is a large solid copper conductor run in the raceway with the conductors feeding the panel but no bonding screw in the bus (obviously because they used it elsewhere).
1 Like
Service panel.