[FONT=TimesNewRoman]Some interesting maximum limits set by ANSI (American National Standards Institute)
• Allowed from unvented space heaters – 200 ppm
• Allowed in furnace flue gas – 400 ppm
• Allowed for emissions from an unvented gas oven – 800 ppm
• Note: All ppm limits above are for “air-free” measurements and all exceed what is considered acceptable “healthful” by all these other testing or oversight organizations.
[FONT=Verdana]Carbon monoxide (CO) concentration in Parts Per Million or as percentage of air
**Parts Per Million **
**% of CO in air **
**Inhalation time and toxic symptoms developed **
0 - 1 ppm
.0001%
Normal background levels
9 ppm
.0009%
Maximum allowable concentration short term in living area (ASHRAE)
25 ppm
.0025%
Maximum exposure TWA (Time Weighted Average) (ACGIH) in the workplace**.**
50 ppm
.005%
Maximum exposure allowed (OSHA) in the workplace**.**
200 ppm
.02%
Mild headache, fatigue, nausea and dizziness.
400 ppm
.04%
**Serious headache - other symptoms intensify. **
Life threatening after 3 hours.
800 ppm
.08%
**Dizziness, nausea and convulsions. **Unconscious within 2 hours, dead within 2 to 3 hours.
1600 ppm
.16%
**Headache, dizziness and nausea. **
Death within 1 - 2 hours.
3200 ppm
.32%
**Headache, dizziness and nausea. **
Death within 1 hour.
6400 ppm
.64%
Headache, dizziness and nausea.
Death within 25 - 30 minutes.
12,800 ppm
1.28%
**Death within 1 - 3 minutes. **
Effects can vary significantly based on age, sex, weight and overall health.
EPAhttp://www.epa.gov/iaq/co.html
CPSC http://www.cpsc.gov/CPSCPUB/PUBS/464.pdf
CO Busters**http://home.att.net/~cobusters1/**
Carbon Monoxide Information Center
Sponsored by First Alert - (312) 337-7773
**Carbon Monoxide Detectors - UL Standard **
"According to UL Standard 2034, home carbon monoxide detectors must sound a warning before carbon monoxide levels reach 100 parts per million over 90 minutes, 200 parts per million over 35 minutes or 400 parts per million over 15 minutes. The standard requires the alarm must sound before an average; healthy adult begins to experience symptoms of carbon monoxide poisoning. The warning provides time to evacuate the premises."
***Note: There are three organizations ASHRAE, ACGIH, and OSHA that rate levels below 100 ppm as unsafe, this is before many home UL Standard ***
CO alarms/monitors/detectors would ever sound for a potential problem.
I often find gas ranges/cooktops with recirculating fans and NO direct exhaust. Although this is allowable I think it is just plain foolish. All other gas fired appliances exhaust to the exterior somehow, except for unvented space heaters.
My experience is, “general elevation of detectable CO with yellow flames.”
You can get a fairly “dirty flame” and still be within ANSI acceptable limits.
Here in lies the problem we may run into.
I call appliance out for elevated/detectable CO emissions.
Seller/realtor gets an appliance tech to come out usually without a CO detector.
Repair person checks “by looking at the flame only” and gives a clean bill of health.
I’m stuck with egg on my face even with all of the information I can provide to the contrary.
I quit taking photos of my CO detector pegged, and just let them know fuel supplied appliance should be vented to the exterior, IMO, and have tech with CO detection adjust and repair to the current standards for that type appliance.
They call me back and say tech said it’s OK I ask "did they use CO detector. No, and there you have it, same sh!t different day.
I’ve found a thorough cleaning of all removable burner components and their ports can make a world of difference in flame color and CO emissions.